Answer / amit kumar sharma
Daily routine test for Diesel Generator
Before Starting
1. Check Fuel Level
2. Check Oil level
3. Cooling Water (For water cooled Generator)
4. Battery Volts and terminals
5. Air Filter
After Starting before loads on
1. Oil Pressure gauge
2. Battery charging ampere
3. Water / Oil Temperature
4. Output supply
5. Output frequency
After Loads on
1. Frequency (check if within acceptable limits)
2. Three phase supply volts
3. Load Sharing on each phase
4. Temperature of Water / Oil
5. Exhaust gas color (Should be clear. Not smoky or black)
IF exhaust gas is black, it is overloaded
If its smoky, oil is leak in manifold, or Diesel quality is
poor
| Is This Answer Correct ? | 41 Yes | 1 No |
Answer / rajendran.m
Battery
Cleaning of terminal and petrolium gelly applied,and to
check a specific gravity of battery.
D.G
To check a battery,water level of radiater, oil level,
diesel level and cleaning of gensets.Will be started a
trail run daily.
| Is This Answer Correct ? | 24 Yes | 2 No |
what is single phase motor?
If load current is 70amps or 50amps what range of CT to install for ampere metering
what is the potential of 11kv A.B.Switch
why do we earth the tandelta point of a power transformer bushing?
how test transfomer(3 phase75kva) by megger
In which working principal temperature transmitter work.explain in detailed.
What are the different losses In a de mac1une'! t.xplam
why transformer fuse wire is very thin as compared to home fuse wire while voltage lavel is low
How many loops can be provided in a circuit as per IS rules.?
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
what is name of transformer oil ?
58 Answers L&T, MPSEB, OPTCL, Practical Viva Questions, Servo, TATA, XLPE, ZGL,
The efficiency figures for energy efficient motors (in comparison with standard efficiency motor) can be generally higher by____%.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)