my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
Yes there's a thumb rule for cable size calculation for 1sqmm Aluminum cable can carry 2Amps and 1 Sqmm Copper wire can carry 4 Amps.
However the cable size increase above 100 Sqmm this thumb rule can not be considered. You need to refer the cable size calculation chart.
| Is This Answer Correct ? | 0 Yes | 0 No |
which stabilizer is better ? AVR, Servo Stabilizer, Static stabilizer etc & why explain it
What is differential relay ? where it can be used?
1 Answers Scope International,
1) name the communication cable and how it is communicate in between plc to modbus , plc with hmi? 2)name of the communication cables?
What are the conditions for sustained oscillator or what is backhouse criterion?
what are the sample questions asking to the test cunducting for electrical superwising lisence test?
what happen if turbine trip ,g.c.b not open and excitation on condition?
How to find out damper winding failure for synchronous machine?
how we can measure the dc current instead of clamp meter ?
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
can any one list the class-a, class-b & class-c trips of power generator?
what is Anti-pumping?
3) How earthing is done? How it measured? Write the method for earthing? How the earth resistance is kept low?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)