my project load is 6 MW so please suggest the size of cable.. ALU 3c 400 aqmm cable can be sufficient.. is there any thumb rule for calculation of cable size please help me
Yes there's a thumb rule for cable size calculation for 1sqmm Aluminum cable can carry 2Amps and 1 Sqmm Copper wire can carry 4 Amps.
However the cable size increase above 100 Sqmm this thumb rule can not be considered. You need to refer the cable size calculation chart.
| Is This Answer Correct ? | 0 Yes | 0 No |
nwhat are the main Components of servo motor?
What is power factor? How to improve Power factor? draw a circuit diagram showing the connection of power factor improvement equipment to the electrical instillation.
if we install two earth pits with a clear space of 5m without any interconnection,by checking the digital multimeter will it show continuity between earth pits? If so what would be the approx. value
Formula to calculate fault current flowing in the neutral line?
where does core based current transformer is used? and what is the value of lux in a work station?
what will be happen if we apply D.C supply to the transformer
what is stacking factor?
what is power plant?
HOW MUCH MAXIMUM CURRENT TAKEN BY NEAUTRAL IN 125 KVA DG SET
what reason of line current and phase current in star connection and line current and phase current not equal in delta connection?
What should do when induction motor take more load in single phase ?
what is difference between electrical and electronics
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)