I have one problem for masoneilan displacer type LT.I give some imformation in data shéet given for liquid level range 0 to 600 mm and sg .955 problem is 0% is ok 25%(23%) or 50%(48%)and 75%(73%) and 100% is ok this is up value and down value all ok so please halpe me
Answers were Sorted based on User's Feedback
Answer / rijesh
i hope that your calibration liquid you using is water[sg=1]. and your service sg=0.955.if so it is give you the output as per your observation
please make your calibration sg and service sg same value.
if you using service sg =0.95 and you using water for a measurement your maximuma span will be 95% and accordingly step change will effect.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad nasarullah khan
Hi Dear.
As you mentioned here taht transmitter's out put 0% and 100% (SPAN) is ok, but inbetween outputs having errror. So you are facing withe " LINEARITY PROBLEM "means out put is not linear , and that always should be linear. so go to linearity section by HART communicator ,hopefully I have answered your question.Regards
| Is This Answer Correct ? | 2 Yes | 4 No |
What is the use of single seated valve?
Consider a level troll. i am getting a correct value in 4mA and 20mA. the value in the middle(30 to 60%)is disturbed and i am not getting the appropriate value. what is the solution to normalize the level and to get the correct value..
why used three wire in RTD.
what do you mean by smart instruments?explain with example
why is the sleeve of the cable used for?
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
What is frequency factor in massflow meter? When using frequency output?
Where Can i take a SPI INtools training in Mumbai? In Rolta India Ltd to whom I should approach regarding of SPI INtools Training?
what is the process for double acting cylinder pneumatic for 32' v/v
How can I map a tank? Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?
what is The specifications for oriface instalation
for oil & gas industries which zone is normally preferred? why? give its example?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)