What is the logic a Transmitter control a Control Valve?
How the signal going to the Control valve?
What are systems/Panels/cables/signal used to control valve
from Transmitter?
Answers were Sorted based on User's Feedback
Answer / gopalakrishnan
IT IS THE CLOSED LOOP ,TX SIGNAL GOING TO THE CONTROL VALVE
THROUGH THE CONTROLLER (DCS) MARSHALLING PANEL -AND TO THE
FIELD JBS AND TO I/P(CURRENT TO PNEUMATIC CONVERTOR AND
THEN TO THE CONTROL VALVE IT IS THE CONTINOUS PROCESS.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / praveen kumar
Well Transmitter Measures the process, and Control valve
will control and this is closed loop. The loop from
Transmitter to JB to MRack to CP and the signal is 4~20mA
but in Control valve we have I/P where the signal will
converted to Pnuematic ok
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / satish
TRANSMITTER WILL GIVEN OUTPUT TO THE CONTROLLER THROUGH
MARSHLLING PANEL THATS CALL PROCESS VALUE,CONTROLLER WILL
GET PROCESS VALUE AS PER CONTROLLER SET POINT THAN FROM
MARSHALLING PANEL THERE IS TWO WIRE/FOUR WIRE SYSTEM AS PER
MARSHALLING CONNECTION OUTPUT WILL GO TO THE CONTROLL VALVE
THAT CALL MANIPLATED VALUE (MV)
| Is This Answer Correct ? | 1 Yes | 2 No |
Explain the difference between plc and cnc?
what is flow equation of kg/hr to m3/hr
Is there is a device to convert mechanical energy to electrical energy
why is an oxygen sensor used in a boiler stack
Can anyone convert a 5/2 way or 3/2 way valve into an ISO valve?
how the 4 to 20 mA signal goes to any controller/indicator,and what is the role of voltage ,12/24 and how to do connection of it, in controller.
Using your own examples solve a problem involving normal table. (experimental method and analysis)
What is the minmum distance between the electrical panel and Instrument panel
How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Instrument QA/Qc what is the project quality plan?conduit inspection RFI. which documents attache with package?
Can anybody please let me know Orifice plate sizing calculation formula and step by step procedure
Calculate the maximum pressure drop that can be allowed to occur across a control valve, so that we can prevent cavitation / flashing from occurring. Use the following formula: Δ P allow = Km (P1 – PvapourA) where, Δ P allow - the maximum allowable differential pressure for sizing purposes, or terminal pressure drop; Km- the valve recovery coefficient from the manufacturer’s catalogue; P1 - absolute inlet fluid pressure; PvapourA - absolute fluid vapour pressure at the inlet temperature; Use Atmospheric pressure = 101.3 kPa, P1 = 1200 kPa(g), PvapourA = 4 kPa, KM = 0.72
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)