Consider a case that two 200 hp motors are connected to 500KVA transformer. For improving power factor can we add capacitors in common bus bars to motors. Or should we add capacitors for each individual motor?
Answers were Sorted based on User's Feedback
Answer / manish panchal
Actually it depends on the motor's actual pf and the load with which motor is connected, so we have to connect capacitor with individual motor according to its pf.
| Is This Answer Correct ? | 4 Yes | 1 No |
Normally, Induction motor current lags the voltage (lagging power factor), to improve the system power factor, we have to add the capacitors in parallel with the load end. Somewhat we can improve the PF to some extend value.
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
Why we find the sensitivity for the CT's to check?
what is purpose of manual bybass in ups
what deffrence between KW $ KVA ?
briefly explain the main blocks found in a microprocessor based system
waht is the working principle of saft starter & what is the difference in vfd & saft starter
what is the function of choke in the flourcent tube lights and why the colour is in white mostly in flourcent tube lights
what do u mean by PS-0.2-5P class of Ct
I am having 120KVA UPS,which is connected to DG & normal power. What is the power drawn by this system when system is running on DG ????
why a motor rating in KW?
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
what is the function of switch gear ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)