What is the impact of MCCB & MPCB on Distributed Control
System?
Answers were Sorted based on User's Feedback
Answer / kasi
MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / manish rane
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.
However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / pyobik
MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / avinash yashwant gunjal
MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / avinash yashwant gunjal
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.
MCCB for protection of distribution system.
MPCB,
overload ,short circuit protection for INDUCTION MOTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harris
How to install ZCT and what is the funtioning for MV Motors?
| Is This Answer Correct ? | 1 Yes | 1 No |
rating of ups??
What will happend if given Vfd out put to step up transformer
1,Building containing 25 flats how much Amp 3 pole MCCB are required? 2, For the safey of each flat how many Amp RCCB can install -loaded with A/C
A transformer is used to light a 24volts,70watts lamp from a 240a.c main.The current in the main cable is 0.35A. Calculate, (1) The efficiency of the transformer. (2) the current in the lamp.
In a tap changing transformer where is the tap connected, is it connected in the primary side or secondary side?
A 2D array X(7,9) is stored linearly column wise in a computers memory.Each element requires 4 bytes for the storage of the value.If the first byte address of X(1,1) is 3000,what could be the last byte adress of X(5,8)?
what is frequency? and its importance
Describe: Energy efficient motors
what is ground clearence in transmission system.is it varies wit conductor size,height of poles,span.
what happens when we give ac supply to the dc motor?and why?
control wiring purpose,standards, ferrule code standard, interlock, schematic, symbol
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)