Answer / kasi
MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.
| Is This Answer Correct ? | 12 Yes | 5 No |
Answer / manish rane
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.
However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection
| Is This Answer Correct ? | 9 Yes | 2 No |
Answer / pyobik
MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.
| Is This Answer Correct ? | 9 Yes | 3 No |
Answer / avinash yashwant gunjal
MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / avinash yashwant gunjal
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.
MCCB for protection of distribution system.
MPCB,
overload ,short circuit protection for INDUCTION MOTOR
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harris
How to install ZCT and what is the funtioning for MV Motors?
| Is This Answer Correct ? | 1 Yes | 1 No |
Differentiate between low pass, high pass and band pass filter?
Simple calculation of improving power factor?
how to check 3phase motor winding with help of multimeter?
The rotor current is directly proportional to slip. How?
Why the TNC switch is called as Memory switch
i have faced a problem in ro plant grunfos make bm30type pump it is 22kw pump. We start this pump using siemens 3rw 4423-ibc44, 30kw softstarter but this soft starter will frequently failier so we planed to change dol starter. So pls tell anybudy its possible or not.
How can a transformer test by megger?
how does capacitor oppose sudden chane in voltage? how does inductor oppose sudden change in current?
4 Answers AAA, Iqra University,
does over charging of a battery reduce its life?
i have done my b.tech in 2009 .still hunting for a job...wat shud i answer if intervevwr asks..(what u have done 1yr)
What is the approximate percentage of Si content in transformer core(CRGO-Cold Rolled Grain Oriented)? Why it is kept so low?
how to calculate transformer load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)