What is the impact of MCCB & MPCB on Distributed Control
System?
Answers were Sorted based on User's Feedback
Answer / kasi
MCBs are miniature circuit breakers with optimum protection
facilities of overcurrent only.These are manufactured for
fault level of up to 10KA only with operating current range
of 0.5 to 63 Amps (the ranges are fixed), single,double and
three pole verson.These are used for smaller loads
-electronic circuits,house wiring etc.
MCCBs are Moulded case Circuit breakers,with protection
facilities of overcurrent, earth fault.it has a variable
range of 50% to 100% operating current.They can be wired for
remote as well as local operation both.They are manufactured
for fault levels of 16KA to 50KA and operating current range
of 25A to 630Amps.They are used for aplication related with
larger power flow requirement.
Is This Answer Correct ? | 12 Yes | 5 No |
Answer / manish rane
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker; Remote operation is major
advantage of both.
However MCCB is use for protection of distribution system &
MPCB is use for INDUCTION MOTOR for protection including
overload ,short circuit protection
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / pyobik
MCCB or the Molded case circuit breaker & MPCB or Motor
protection circuit breaker; their effect on the distributed
control system is that they are remotely accessible from
the control room, they can either be switched on or trip
from the control room itself.
Is This Answer Correct ? | 9 Yes | 3 No |
Answer / avinash yashwant gunjal
MCCB- 1 Protection of power & control ckt.
2 protections- A)overcurrent B)earth fault
3 op.current- 25-630 amp
MPCB- 1 Provides motor protection (AC motor)
2 Protections- A)thermal overload B)magnetic short
ckt.
3 op.current-o.1 A- 25 A
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / avinash yashwant gunjal
MCCB is Molded case circuit breaker & MPCB is Motor
protection circuit breaker.
MCCB for protection of distribution system.
MPCB,
overload ,short circuit protection for INDUCTION MOTOR
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / harris
How to install ZCT and what is the funtioning for MV Motors?
Is This Answer Correct ? | 1 Yes | 1 No |
What will be electrical cost per sqft for IT building (basebuild and fitout)and for residential township?
how to flameproof electrical motor on the shaft?
Can we connect CBCT in the Busduct
what is the function of RMU?
What will be the average KVA rating of Auto Transformer for 75kw 415V , 3phase induction motor
how much current capacity 250 amp. mccb please tell me about whats are the reasons to trip 2 or 3 times in a night. and what are the steps to short out this problem
how you configure motorvision relay (L&T make)from DCS
can I connect 25KvA stepdown transformer(RYB-440V,UVW-240V) to the output of 15KvA,3-phase online UPS(440V phase to phase)please brief.
What is the meaning of EDO in DG panels?
what is difference between differential protection and distance protection and how we calculate the sloop?
What is the function of RCBO? What are the different sensitivity ratings & each application?
Why the output of generator varies eventhough the shaft speed is constant in thermal power plant?