Answer / gopal
actually here we are dealing with phasors in AC system .and
Vs and Vr are equal in magnitude but not in phase angle.
power flows from Vs/_ᵟ to Vr/_0 according to the equation of
real power flow
P= Vs Vr Sin(ᵟ) Vs/_ᵟ - Vr/_0
------ = ---------------
Xs I
actually in phasors although their magnitude is equal but
still their difference is not zero and an appriciable
voltage difference exist between the two ends which trigger
current and hence power to flow,
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / akash kumar
actually for the transfer of active power in a ac transmission system you need phase difference between the Vs and Vr.a line loaded with its own surge impedance acts as of reactive nature only.its reactive power requirement is supplied by its own line capacitance.thus no reactive component of line current and hence highest ohmic current in the line!!!
P=(Vs*Vr/X)Sin(delta)
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / muhammad ismail
Actually you are asking about Vs and Vr and PD.
On load side there is always ZERO Potential thats why power
flows to receiving side in line.
| Is This Answer Correct ? | 0 Yes | 1 No |
Can the field winding in synchronous machines be placed on stator?What is the limitation of such arrangement?
What are the methods used to improve powerfactor ?
what is the healthy specific gravity of lead acid battery used in DG sets ?
3 Answers Bhushan Power Steel,
my field of interest is T&D. plz tell something about that.
Is a contactor (or master relay) required between incoming lines and a VFD? The question goes to safety. If a contactor were used before the VFD and an e-stop engaged then the motor will coast to a stop (i.e. VFD loses power) instead of stopping much faster if the VFD braking fucntion were used. It would make more sense to keep power on the VFD.
Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.
why ac signals are sinosuidal
Slow acting fuses are most often used for which application a) Lighting circuit b) heating circuit c) Motor D) Radar circuit
I have two power supply.a)govt. power b)Captive power.3 phase load connected inside factory.when source change govt. source to captive some motor rotate reverse. Is phase sequence changes when if off & on?If I off generator & on it again is it possible to get changed phase sequence??
what is per unit calculation?looking for simple and strong explanation thk u
Why Powers are named in MW?
Which type of transformer used in lighting load?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)