Kindly give the brief explanations for checking 12.5 kvar
440V, 25 KVAR 440V, 12.5KVAR 690V, 25 KVAR 690V capacitors
microfarad values. what is the microfarad values for the
above four type of capacitors, and give the formula
explanations briefly. I know F-50HZ, voltage, and capacitor.
1)If this is only 1 capacitor and this is the voltage
between capacitor terminals:
Cap=10^9*Q/(Voltage^2*2*pi*frequency) if Q is in kVAR and
capacity in microFarad.
pi=3.14159
Cap=10^9*12.5/(440^2*2*pi*50)=205.5 mF
2)If this is reactive power of 3 capacitors in Y connection:
Voltage at a single capacitor terminals will be 440/sqrt(3)
=440/1.73=254 V
Reactive power of a single capacitor will be 12.5/3=4.167
kVAR
Then the capacity of a single capacitor will be :
Cap=10^9*4.167/(254^2*2*pi*50)=205.5 mF
3)If this is reactive power of 3 capacitors in Delta
[Triangle] connection:
Voltage at a single capacitor terminals will be 440 V
Then the capacity of a single capacitor will be :
Cap=10^9*4.167/(440^2*2*pi*50)=68.5 mF
If Q=25 kVAR Voltage=440 V then the capacity of a single
capacitor will be :
single and Y=411 microF ; Delta=137
If Q=12.5 kVAR Voltage=690 V then the capacity of a single
capacitor will be :
single and Y= 83.6 microF ; Delta=27.85
If Q=25 kVAR Voltage=690 V then the capacity of a single
capacitor will be :
single and Y= 167 microF ; Delta=55.7 microF
Is This Answer Correct ? | 1 Yes | 0 No |
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
Hi.I want to ask how to calculate contactor rating current? for example I have 460 V , 100 A (induction motor) calculate contactor rating current?
how pt is using
The shot circuit in any winding of transformer result? Explain
What is the reason of polyphase induction motor tripping suddenly on high current during running at 70% laod? Motor IR , winding resistance & inductance balance. Motor no load current is balance and ok as per mgfr. data.
who iz power minister ?? :P
1) Explain why we don't link the two earthing system ht and mv on a pole mounted transformer sub-station.
what is suitable alternative for an igbt?
what is control supply rating of a machine
What is making & breaking current ???
High Voltage out door substation-annual maintenance, things to be considered
a. void main() { char a[6] = "INDIA"; while(*a) { printf("%c",*a); a++; } } 1. india 2. I N D I A 3. no output 4. error 5.Null