Kindly give the brief explanations for checking 12.5 kvar
440V, 25 KVAR 440V, 12.5KVAR 690V, 25 KVAR 690V capacitors
microfarad values. what is the microfarad values for the
above four type of capacitors, and give the formula
explanations briefly. I know F-50HZ, voltage, and capacitor.
1)If this is only 1 capacitor and this is the voltage
between capacitor terminals:
Cap=10^9*Q/(Voltage^2*2*pi*frequency) if Q is in kVAR and
capacity in microFarad.
pi=3.14159
Cap=10^9*12.5/(440^2*2*pi*50)=205.5 mF
2)If this is reactive power of 3 capacitors in Y connection:
Voltage at a single capacitor terminals will be 440/sqrt(3)
=440/1.73=254 V
Reactive power of a single capacitor will be 12.5/3=4.167
kVAR
Then the capacity of a single capacitor will be :
Cap=10^9*4.167/(254^2*2*pi*50)=205.5 mF
3)If this is reactive power of 3 capacitors in Delta
[Triangle] connection:
Voltage at a single capacitor terminals will be 440 V
Then the capacity of a single capacitor will be :
Cap=10^9*4.167/(440^2*2*pi*50)=68.5 mF
If Q=25 kVAR Voltage=440 V then the capacity of a single
capacitor will be :
single and Y=411 microF ; Delta=137
If Q=12.5 kVAR Voltage=690 V then the capacity of a single
capacitor will be :
single and Y= 83.6 microF ; Delta=27.85
If Q=25 kVAR Voltage=690 V then the capacity of a single
capacitor will be :
single and Y= 167 microF ; Delta=55.7 microF
| Is This Answer Correct ? | 1 Yes | 0 No |
what are the limitations to use 33kv ac in industries?
why high speed tripping relay will be used in tripping circuit why not normal relay
What is the function of Buchholz relay in transformer ?
why America use 60HZ 110V?
why transmission line towers are longer than communication line towers?
how to find the resistance
how calculate kva in to kw
Either the Armoured Earthing strip of HT 3 core cable have to pass through CB CT or not , why ???
what happens when we give ac supply to the dc motor?and why?
what is the difference between DOL starter&star-delta starter& automatic star-delta starter
How to calculat size of copper & aluminium ?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)