Answer / aditya shirbavikar
The rating of any circuit breaker is decided on the basis of its breaking capacity. so, the KA rating of MCCB is the unsymmetrical breaking capacity for a particular time.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s.lenin
The KA Rating of MCCB is Defined as maximum current flowing
through the conductor or with standing capacity of the
breaker.the KA is decided mostly that incoming transformer
fault current
| Is This Answer Correct ? | 1 Yes | 0 No |
The value of the kA rating determines how much current the circuit breaker can withstand under fault conditions. The circuit breaker only has to withstand this for a brief period of time, usually the time it takes for the circuit breaker to trip. For example, a value of 6kA means that the circuit breaker can withstand 6,000 amps of current during the brief time it takes to trip.
| Is This Answer Correct ? | 1 Yes | 0 No |
What are the difference between these terms ? e.m.f, voltage, potential, potential difference, current etc? what are the difference between these terms ? (electromotive force) e.m.f, voltage, potential, potential difference, reference potential, reference potential difference, current. How can i explain and describe these all terms in single line each and little more explaination too thanks
What are the causes of unbalanced current on 34.5kv feeder Ia=0.05,Ib= 0.25, Ic=0.15 and In=0.27 prior to tripping current are balance?
what happen if drive input fail momentry at 48.5 HZ frequency?
what causes contact chatter when there is no demand on the air conditioning unit?
What is the necessary and sufficient condition for stability.
if any body have question paper of railway (section engineering),then plz send me .i will thank of him/her.
What is the pratically meaning of neagative going ac current.
Why Delta Star Transformers are used for Lighting Loads.
what is the requirement of commutator in a universal motor?
how many earthing required for ups, what should be the earth voltages
Can we parallel lise the secondary side of the two similiar transformers with same voltage ration, imp, but with different vector groups.. ( for ex. 11 KV / 6.6KV two trfs but different vector groups can we parallelise both of them ,, what happens if we parallelise them
IF we have 500kva transformer 11.0/0.415V, 50Hz. How to calculate the current on HT & LT side, how can we consider for its breaker (HT & LT both)? You are requested to solve the question herewith.
3 Answers Bhutan Power Corporation,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)