Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


What is meant by GAP VOLTAGE, in vibration measurement.
Normally how much GAP VOLTAGE is set and state the reason.

Answers were Sorted based on User's Feedback



What is meant by GAP VOLTAGE, in vibration measurement. Normally how much GAP VOLTAGE is set and s..

Answer / mazari

Gap voltage of Bently Nevada vibration probe is usually set at -10V. Reason for setting at -10 volt is as we know, proximitor allows probe to work -2 volt to -18 volt. So voltage difference of 2 to 10 and 10 to 18 is 8 volt. When setting at -10 volt, probe can equally measures vibration at both sides(I mean when shaft is going away from probe or towards probe).
Suppose we adjust probe at -9 volt. Probe can detect vibration?
Yes, it can can detect vibration but its one side will be margin of 7 volt and other side margin of 11 volt. At 11 volt margin, probe will detect vibration excellent but at other side,7 volt side, it has limitation, when more vibration it may not detect.
(Old system, when proximitor supply was 18 volt, setting were at -8 volt, now such proximitor almost obsoleted)
aftabmazari@yahoo.com

Is This Answer Correct ?    23 Yes 2 No

What is meant by GAP VOLTAGE, in vibration measurement. Normally how much GAP VOLTAGE is set and s..

Answer / arshad.aes@gmail.com

gape voltage is set 10v.if sensor is old that time we adjust
at 8 -10v.in this case also we adjust the gape between sensor
and target it is mostly 1mm to 0.9mm.

Is This Answer Correct ?    16 Yes 3 No

What is meant by GAP VOLTAGE, in vibration measurement. Normally how much GAP VOLTAGE is set and s..

Answer / bubun

The voltage proportional to the gap between proxy and the target material is gap voltage.generally 0 to 10 V dc.

Is This Answer Correct ?    5 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

How to work togather like sov,limit switch,proxy switch and booster in xv

0 Answers  


Using your own examples solve a problem involving normal table. (experimental method and analysis)

0 Answers  


A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.

0 Answers   MNC,


Why we not use 2-20Ma or 1-20Ma

5 Answers  


What is the purpose of LO Overhead tank in turbines.

0 Answers   ADMA OPCO,


How to decrease opening & closing time of on/off valve?

0 Answers   UPL,


protection relay watchdog contact operation?

0 Answers   L&T,


How to calculate flow of air bubbler type level transmiter  According hight and density 

2 Answers   Qatar Petroleums, RKS,


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


TECHNICAL/ARTITUDE

0 Answers   ONGC,


What are primary elements of measuring pressure?

0 Answers  


can we replace a pressure transmitter of range 0 to 25 Kg/cm2 by a Pressure transmitter of range 0 to 10 Kg/cm2 ?.. Will it affect 4 to 20 mA output signal which we will feed to the PLC.

9 Answers   IOCL,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)