30 kVA and voltage 380/220VAC how to find out kA?
Answers were Sorted based on User's Feedback
Vipul Kumar your answer is wrong.
W is not = 1.732x380xI. W =1.732x380xIx PF. You left off
the power factor
Bala your answer is wrong also.
KA is not equal power/ (1.732*400*% of Impedance)Note
spelling of impedance. Where did you go to school?
Amps = 30 KVA/ (0.380 x 1.73)or 30000 va/380 x 1.73
Amps = 46
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / simon
30Kva=30,000va
30,000 VA=440V*68.1818 Amp*1 (Pf)
Hense Ka=0.068
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / vipul kumar rai
W=1.732x380xI
30x1000=1.732x380xI
I=30000/658.16
I=45.581 ( FOR THE PRIMARY CURRENT )
W=1.732x220xI
I=78.731 ( FOR THE SECONDRY CURRENT )
| Is This Answer Correct ? | 1 Yes | 3 No |
Answer / bala
we need to know the Impedance of the TxR.Becos the Formula for Determine the KA value is
=power/ (1.732*400*% of Impedence)
For EX-
Power = 1500 KVA
Voltage = 400V
Impedance = 6%
short circuit = 1500*1000/(1.732*400*0.06)
= 36085A or 36 KA
| Is This Answer Correct ? | 0 Yes | 2 No |
what is different between auto transformer and vriac
Does all the output contacts (N/O as well as N/C) of a Numerical relay operate when relay receives a binary input/inputs or contacts are designated to specific logic input/inputs and only these contacts operate?
what is a difference berween line voltage and phase voltage?
what happen "when Dyn11 is parallel operation with Dyn1"?
HOW THE AC GENARATOR CAN GENARATE REACTIVE POWER,HOW CAN WE CONTROL IT.AND OTHER SOURSES OF REACTIVE POWER GENARATIONS ARE WHAT.
how do you select the ct/pt rating in substation
1 Answers Apollo, Shreem Electric Ltd, Tata Motors,
how will we calculate the copper wire load..
If i am running of spindle at 2000rpm ,but How to spindle stop at the second I am resetting the machine in CNC machines
We have 11kV/110V three phase indoor potential transformer in 66/11kV Sub-station, where the failure of PT is frequently happening and the rating of the PT is 0.2 class accuracy, with primary star and seconday (two cores) star connected. Some experts has suggested to not to connect the PT Primary neutral to the ground because when transformer neutal NCT connection is loose; the faulty current will flow through the PT primary neutral, resulting into failure of PT. My question is: Is it necessary to remove the primary neutral connection of the PT from ground? if not, what would be the reason for failure of PT. Please guide me.
what is the contact resistance of Air circuit breaker??
What is applied voltage for meggering a 6600V HT cable
1)why the transformer rating in KVA insted of KW 2)why the secondary of ct is shorted and why the PT secondary is open
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)