Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Why the transformers are rating in KVA.?

Answers were Sorted based on User's Feedback



Why the transformers are rating in KVA.?..

Answer / panda171


Power given to the transformer is Apparent power (K)
it is the supply power of the power house and the power
given by the transformer to the Load is the true power or
Active power which is actual used by the load and rest is
the reactive power i.e. square of apparent power including
iron loss & copper loss in KVA = square of true power in KW
+ square of reactive power in KVAR. A sound transformer
efficiency is 98% (input power- Iron loss (k) & copper loss
= output power).
For full resistive load (at unity pf ) a 100 KVA
transformer gives 100 KW (approx.) true power, and for
inductive power at .8 pf the same will able to give 80 KW
(approx.) true power, but the types of load (its pf) is not
know before which to be connected across the transformer,
this is only why the transformers are rated in KVA and it
is meaningless to discuss about the iron loss and copper
loss because the Inventor and UPS are also rated in
KVA.

In other hand or in simply we can
say due to unknowing power factor the transformer,
generator etc are rated in KVA. In heavy size transformer
copper loss is more and it vary with load and Climate
i.e. transformer oil condition but it is not reason to
rating the transformer in KVA.


P.C. Panda (BRG)
Mob 9938431756

Is This Answer Correct ?    7 Yes 0 No

Why the transformers are rating in KVA.?..

Answer / rvd.chakkara

Transformers are not depends upon the Power Factor. So, it is named as KVA and not as KW.

Is This Answer Correct ?    3 Yes 0 No

Why the transformers are rating in KVA.?..

Answer / hitesh gohil

Copper Loss and Iron Loss

Is This Answer Correct ?    3 Yes 2 No

Why the transformers are rating in KVA.?..

Answer / sujit kumar sah, nitn

As we know Copper Loss of a transformer depends on Voltage and
Iron Loss depends on volt-ampere not on phase angle between
voltage and current i.e the rating of a transformer is in KVA

Is This Answer Correct ?    1 Yes 1 No

Why the transformers are rating in KVA.?..

Answer / irfan ahmad dar

bcoz in transformer actually there are two types of core losses and copper loss
which depend upon voltage and current but not upon power factor
so that is why transformer is rated in kv not in kwi

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How can be decreased the size of transformer?

6 Answers  


what will happen if field winding of Synchronous generators given ac supply

4 Answers  


Befor synchronissation of Generator what test to be carried out.pl.specify with reason.

3 Answers   Kanoria,


what is called star connection and delta connection also purpose of this connections?

3 Answers   Siemens,


why eee branch?

1 Answers   TCS,


Hi, i want to know is meant by power quality? How it can calculated ? How we can improve?

1 Answers  


how gen. load increase or decrease ? what happen with gen on that time

2 Answers  


why we use CVT (capacitive voltage transformer)in switch yard?

5 Answers  


what you mean by current? what you mean by voltage? what is difference between star and delta connection in motor side?

2 Answers   Adani,


why vector group used in transformer and what effective in output

1 Answers  


What are methods to avoid the inrush current at the time of starting of power transformer ?

8 Answers   Wipro,


why series motor cannot be started on no-load?

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)