if we open the inlet of an air regulator ,how it will affect
the out put of regulator? (out put of regulator is using to
operate an on-off valve.it is an air to open valve,and valve
is in open position.my doubt is air regulator will hold the
valve in open or not,if there is no consumption or leak in
regulator out put side ,we only loose the input pressure.)
Answers were Sorted based on User's Feedback
if you open the inlet of afr, valve ramains in open condition only, bcoz afr hold the output air pressure until u drain from regulator. and you are telling that while you are going to open the inlet of air regulator your valve is in open position, that means there should be air in outlet of regulator. bcoz your valve is air to open valve. if there is no air it should be in close condition.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / mallu byali
AFR DOES NOT HOLD THE PRESSURE, IT IS ONLY REGULATE THE
PRESSURE AS YOUR DESIRED SET POINT OR WE HAVE TO SET THE
PRESSURE FOR OPERATING THE VALVE DEPENDS UPON ITS ACTUATOR
CAPACITY..
Is This Answer Correct ? | 6 Yes | 5 No |
Answer / girish.bashyam
Regulator is just for regulating the air supply . this air
supply will be regulated as per the name plate detail of
control valve. the output of AFR will go to positioner and
its output will go to diaphragm. Depends on the mA the
flapper will be moving and accordindly the output of
positioner will vary its outputis connected to diaphragm
which will move from 0 to 100% respective of the command.due
to flapper movenment the required air to move the diaphragm
only provide to diaphragm for its movenment.
Is This Answer Correct ? | 2 Yes | 5 No |
Answer / sandeep modi
If you open the inlet of air regulator,no pressure will hold
at air regulator,the pressure will go to zero and your air
to open valve will close.
But when you stop the supply of inlet air(not open the
supply) the pressure of AFR will be hold at that
condition,and if you valve is in open condition ,it will
remain open.
Is This Answer Correct ? | 0 Yes | 3 No |
give eg of how I/P is used in control loops
plz send me general of ongc
what is difference between HOT permit and cold permit
What is the Difference between CNC and PLC
How to calculate the flow rate in Vortex flow meter?What is K factor?Can you give me an example calculation to understand the same as better?
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
What is difference between profibus and modbus communication
What are different types of cable?
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
Hi friends, from Aug 4th onwards iam getting spikes for analog inputs in our DCS for a period of 800ms. I throughly checked every thing, finally i found that the DI, DO's from MCC panels shields are terminated in the Signal Earth where Analog Input signals shields are terminated. Is there any problem with this type of termination?. i checked the induction voltage from MCC and getting around 25VAC, please suggest me in this concern. Our plant is 8months old only. DCS is Siemens Make Simatic PCS7, and the transmitters are Yokogawa make.
What is meant by Fail Safe Condition in PLC?
why orfice is not used for main steam flow calculation