how to calculate the earthing conductor & no. of earth pits
required
Answers were Sorted based on User's Feedback
Answer / mrutyunjay mohanty
Dear Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrutyunjay
Dear Sudhakar Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault) as per IS 3043
Is this equation to be taken for all types of electrodes ( Plate, Rod or Pipe & Strip ) ?
Because , as per IS 3043, same equation is appropriate for plate electrode
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar.g
The earth resistance of single rod or pipe electrode is calculated as per IS 3040:
R=100xρ/2×3.14xL (loge(4xL/d))
Where:
ρ = Resistivity of soil (Ω meter),
L = Length of electrode (cm),
D = Diameter of electrode (cm)
Example:
Calculate number of CI earthing pipe of 100mm diameter, 3 meter length. System has fault current 50KA for 1 sec and soil resistivity is 72.44 Ω-Meters.
Current Density At The Surface of Earth Electrode (As per IS 3043):
• Max. allowable current density I = 7.57×1000/(√ρxt) A/m2
• Max. allowable current density = 7.57×1000/(√72.44X1) = 889.419 A/m2
• Surface area of one 100mm dia. 3 meter Pipe = 2 x 3.14 x r x L = 2 x 3.14 x 0.05 x3 = 0.942 m2
• Max. current dissipated by one Earthing Pipe = Current Density x Surface area of electrode
• Max. current dissipated by one earthing pipe = 889.419x 0.942 = 837.83 A say 838 Amps
• Number of earthing pipe required = Fault Current / Max.current dissipated by one earthing pipe.
• Number of earthing pipe required = 50000/838 = 59.66 Say 60 No’s.
• Total number of earthing pipe required = 60 No’s.
• Resistance of earthing pipe (isolated) R = 100xρ/2×3.14xLx(loge (4XL/d))
• Resistance of earthing pipe (isolated) R = 100×72.44 /2×3.14x300x(loge (4X300/10)) = 7.99 Ω/Pipe
• Overall resistance of 60 no of earthing pipe = 7.99/60 = 0.133 Ω.
If you have any doubt regarding this ...pls mail me sudhakar28485@gmail.com
| Is This Answer Correct ? | 4 Yes | 5 No |
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
0 Answers Bhel, Jai Balaji, Rashmi Group,
what id a dry type transformers and its function ?
How do you select a cable size(Cu & Al) for a particular load?
What is the meaning of GRID?
what is OLTC and difference between RTCC and OLTC
IF ANY MATERIAL AVAILABLE IN MARKET FOR MOTOR PROTECTION INSTEAD OF OLR & CONTACTOR ?
how to calculate the conductor size for certain KV transmission line and distribution line?
A circuit breaker is a
why do we use magnetic contactors ?circuit breakers are not enough?
what is value of Jin transformer
what is a tri vector meter? what are the tri vectors?
how to calculate power loss cost of aluminium conductor and copper conductor?500v,100A,68mm area squre busbar.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)