Answer / mrutyunjay mohanty
Dear Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mrutyunjay
Dear Sudhakar Sir,
Greetings of the day !
Recently I have been through one answer shared by you and got your email id at AllInterview.com. Please kindly help me in my below concern :
Permissible current density equation i = (7.57*1000) / sqrt(resistivity * duration of earth fault) as per IS 3043
Is this equation to be taken for all types of electrodes ( Plate, Rod or Pipe & Strip ) ?
Because , as per IS 3043, same equation is appropriate for plate electrode
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sudhakar.g
The earth resistance of single rod or pipe electrode is calculated as per IS 3040:
R=100xρ/2×3.14xL (loge(4xL/d))
Where:
ρ = Resistivity of soil (Ω meter),
L = Length of electrode (cm),
D = Diameter of electrode (cm)
Example:
Calculate number of CI earthing pipe of 100mm diameter, 3 meter length. System has fault current 50KA for 1 sec and soil resistivity is 72.44 Ω-Meters.
Current Density At The Surface of Earth Electrode (As per IS 3043):
• Max. allowable current density I = 7.57×1000/(√ρxt) A/m2
• Max. allowable current density = 7.57×1000/(√72.44X1) = 889.419 A/m2
• Surface area of one 100mm dia. 3 meter Pipe = 2 x 3.14 x r x L = 2 x 3.14 x 0.05 x3 = 0.942 m2
• Max. current dissipated by one Earthing Pipe = Current Density x Surface area of electrode
• Max. current dissipated by one earthing pipe = 889.419x 0.942 = 837.83 A say 838 Amps
• Number of earthing pipe required = Fault Current / Max.current dissipated by one earthing pipe.
• Number of earthing pipe required = 50000/838 = 59.66 Say 60 No’s.
• Total number of earthing pipe required = 60 No’s.
• Resistance of earthing pipe (isolated) R = 100xρ/2×3.14xLx(loge (4XL/d))
• Resistance of earthing pipe (isolated) R = 100×72.44 /2×3.14x300x(loge (4X300/10)) = 7.99 Ω/Pipe
• Overall resistance of 60 no of earthing pipe = 7.99/60 = 0.133 Ω.
If you have any doubt regarding this ...pls mail me sudhakar28485@gmail.com
| Is This Answer Correct ? | 4 Yes | 5 No |
WHAT IS EXTENDED DELTA AUTOTRANSFORMER? WHERE WE USE THAT?
Whis machine is having higher efficiency Transformer or Generator
How to do the REF Stability test for power transformers in Site?
how can electricity is produced without water
what is the use of spst switch in performing experiment on self excited dc motor?
what are symmetrical and non symmetrical components in electrical installation.
What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?
What happens if the capacitive reactance of a transmission line is very high?
rating of ups??
my question is how to answer the question "you are from b.tech eee background and why do you want to go for banking
Damping resistor provided in open delta (tartiary) winding of a measuring PT at the incoming of a MV inverter drive panel is getting heated up. Can any body explain the reasons and suggest the remedy?
How you take care of a motor from over loading and what are the different overloading ratings of different motors?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)