if an induction motor is operated at unity power factor what
will happen? will motor run or not? kindly describe a
logical answer?
Answers were Sorted based on User's Feedback
Answer / vipul jain
In the case starter, the capacitors are often controlled by
the main contactor which is also controlling the motor.
This is because the capacitance and the inductance of the
motor form a resonant circuit. While the motor is connected
to the supply, there is no problem. Once the motor is
disconnected from the supply, it begins to decelerate. As it
decelerates, it generates voltage at the frequency at which
it is rotating. If the capacitive reactance equals the
inductive reactance, i.e. unity power factor, we have
resonance. If the motor is critically corrected (pf = 1) or
over corrected, then as the motor slows, the voltage it is
generating will pass through the resonant frequency set up
between the motor and the capacitors. If this happens, major
problems can occur. There will be very high voltages
developed across the motor terminals and capacitors causing
insulation damage, high resonant currents can flow, and
transient torque's generated can cause mechanical equipment
failure.
Is This Answer Correct ? | 9 Yes | 2 No |
Answer / g.v.hema chandu
The unity power factor means the angle b/w voltage and current is unity.As a practical it is not possible for motors because motor is inductive.For an theory if motor is at unit power factor the speed decreases.
Is This Answer Correct ? | 0 Yes | 0 No |
how the testing of CT OF 400/200/100 done in33/11 kv s/s
i Have 1000kva 11/.4 kv voltemp make t/f Its a 2 year old. i wants to known how much iron losses & copper loses during no load condition.
What is the output voltage of a DG set.
What is the difference between relays and contactor construction wise?
in general it is observed in power stations, the tertiary winding is used in higher rating Y-Y auto transformer but not in Y-Y power transformer. is the tertiary winding is compulsory then why it is not using in power transformer
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
In a 132KV Grid Station where voltage level is 132KV, here, why the rating of Surge arrests installed 120KV ?
why distribution transformer is uesd in Delta/Star formation?is there any significance in doing this?If yes then breif?
How can calculate HT side VCB? For example I have 1250 KVA load what will be HT side VCB Amp.range and what size XLPE cable I use for HT side.
2 Answers NASSA, Orchid, SB Automation,
How to determine the short circuit current for breakers and VCB.
what happen to a dc series motor if it given as ac supply accidentaly
why transformer is rated in kva?