What will be the effect of in HT XLPE 220 KV
cable when one side of the Armour/cable ends are not
grounded. Will there is difference between 3-phase voltages?
like: if
A. Both End of Cable grounded Phase Voltages:- V1=219 KV,
v2=220 Kv, v3=220 KV.
B. One End is grounded other is not: than Impact on Phase
Voltages:- V1= KV, v2= Kv, v3= KV. Remain same or
unchanged??

Answer Posted / hemant

mostly we consider that armour is given for machanical
protection to cable from any type of hard punching on cable
and other if cable get damaged then it touch to armour
which alredy connected to ground hence our differantial
reley get pick up and device which connect to ht cable is
protected. if both end of armour is connected to ground
there may not any effect to supply voltage in cable it
depend upon cable insulation. only leakage current get
discharge via armour to ground. hence in point of me trere
is no one effect on 3 phase voltage it also remain same.
one thing is that armour one end require to connect ground
and second to device for earthing to device.

Is This Answer Correct ?    2 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What will happen if we on 200kvr capacitor bank(11kv in bus)If there is low load on transformer (1.5 mva 33/11 kv)

1120


draw the block diagram of fire alarm?

4988


What are the types of piano switches?

1436


Type of motor stater detail and working detail

1265


I am going to appear RRB Sr. Section Engineer Exam, Electrical. Can you send me previous year questions of RRB Electrical engineer. specially Section Engineer questions. my email id is likerahulworld@gmail.com

1363






If two Transformers are connected in parallel having impedance of 50KA in both transformers will the impedance increase or decrease after connecting transformers in parallel?

1539


What are the three types of compensators?

637


what is the meaning of number in (11, 31, 61,14, etc. CDG11, CDG31, CDG61, DDT32

901


what does mean of RCT and STR in diffrential CT?

3764


In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?

1719


What are the commonly used schemes for the bus zone protection?

545


Explain dc generator with its types?

634


Define the term Capacitance and Inductance?

649


USE OF 8 WAY PAN ASSEMBLY

1495


What range of speed can you get with the field control method of speed control of d.c. Shunt motor?

666