Answer / sunil kumar sinha
Shaft of large motors need to be insulated at one end and
earthed at other end.Due to some unbalance in electrical
system (Which can not be avoided)very small amount of
voltage induces along the rotor shaft. One end of shaft is
normally earthed through carbon brush or through earthed
bearing, hence one end of rotor shaft is anchored at earth
potential and other end will float and experience small
voltage w.r.t earth as voltage is induced along the shaft.
Now the shaft is supported on bearings. One
end of bearing is either earthed if no earthing brush is
provided and the other end support bearing is insulated.The
insulation resistance of shaft, by lifting earthed beating
end of the shaft is to be measured to ensure that the
insulated bearing is healthy. This is to be measured during
assembly of motor because the healthy mess of insulated
bearing can be checked at this stage only.
Further when motor is in operation shaft voltage is to be
measured. Some voltage must appear. If there is no voltage
it indicates that the insulated bearing has also earthed.
this will make path for shaft current to flow through the
bearings. this will result in pitting of babit of bearings
and finally its failure, increase in shaft vibration.
Hence for healthiness of support bearings of motor current
insulation is must and need to be checked periodically for
healthyness of motor rotor bearings.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avd
In large motors both bearings needs to be insulated to
avoid flow of current through bearings.This flow of current
is caused in rotor due to high flux in the large motors. If
current flows through bearings there will be pitting in the
bearings and will cause premature bearing failure. To give
path to current, genaraly carbon brushes are used at motor
shaft which are grounded at other end.Hence flow of current
through bearings avoided.
After assembling of motor on bearing padastal both
bearings insulation resistance shall be checked by megger.
| Is This Answer Correct ? | 0 Yes | 0 No |
what are the energy savings methods that are existing in coal based power plant?
If genrator not build up voltage , How u can Manually Excite ?
What is difference and reason b/w -48V BTS system and 24 V BTS system. Plzzzzzzzzz tel me.
what is the application of dynamic Breaking resistor in inverter ? & How it works ?
what kind of technical test that i need to learn because i have an interview tomorrow.. please someone help me..
What is the best thing to protect the motor from running over full current. CT or O/L or pressure transducer at the given pressure rating
how is the many rpm of acb charging motor ?
Why MS rod or flat are used in stead of GI rod or flat in switchyard earth mat ?
what is the full form of KVAR
what is the difference between ground, earth and neutral?????????....
why crgo core is used in transformers?
How the unidirectional torque produced in dc motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)