how i meggar value of 11kv alternator winding.and with meggar.



how i meggar value of 11kv alternator winding.and with meggar...

Answer / kj

See extract from service manual for HV alternator.

A 5000V motorised megger or similar instrument should be
used. Separate the three neutral leads,
ground V and W leads and megger U to ground. Repeat for V
phase with U and W grounded and W
phase with U and V grounded. Minimum acceptable limits
after 1 minute for each phase are:
New machine 300 M
In-service machine 150 M
The insulation resistance should not be less than specified
and the polarisation index should be in the
order of 2 or greater at 20 ÂșC.
(PI = IR10min / IR1min)

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

what is the iron loss in a 11KV/440V transformer?

2 Answers   Bhel, TVS,


IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM

0 Answers  


1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.

1 Answers  


what is the MF if CT ratio is 500/5 and in meter specification is 3.75 REVS/KWH? Thanks and Regards Selvendran.N

1 Answers  


What are the functions of different probes used in cro?

0 Answers  






What are merits & De-merits of State-Space Method? What is series programming, parallel programming, general programming & direct programming ? And, difference between these programmings Techniques ?

0 Answers  


what will be the minimum megger value for 132 Kv (earthed) potential transformer

3 Answers  


What is cable size of motor if starting current is 15.6 Amperes??

0 Answers  


How to calulate Voltage Drop for perticular lentgh of busbar (Cu/ Al)?

1 Answers  


Can I use 1 phase power supply to run 3 phase motor? If yes, how?

6 Answers  


In a parallel circuit dc circuit with two resistors, if you know the voltage, amperage, and one resistors ohms, what formula is used to find the second resistors ohms?

6 Answers  


what is the function of NAT & NAC contacts in breaker control switch (TNC)??

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)