Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to calculate short ckt current of trafo.
ex.3-ph 3MVA trfo. 11/440, impdence voltage=7.25%



how to calculate short ckt current of trafo. ex.3-ph 3MVA trfo. 11/440, impdence voltage=7.25%..

Answer / annonymous

Fault MVA = 3MVA/0.0725= 41.38MVA

So fault current on 11kV side= 41.38/(1.732x11x0.8)= 2.715kA

fault current on 0.440kV side=41.38/(1.732x.44x0.8)= 67.87kA

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

why total tape position are odd in number in Power transformer ?

1 Answers  


A resistance of 50 kΩ has a conductance of:(a) 20S(b) 0.02S(c) 0.02 mS(d) 20 kS

1 Answers  


Why slip ring ind. motor power consumption is low compare to induction motor .same 90 kw motor used same load output

0 Answers   Altra Power,


Why in india freq. is 50HZ & in U.S.A. it is 60HZ?

2 Answers   MacLellan,


The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?

0 Answers   PGVCL Paschim Gujarat Vij Company Limited,


how to calculate the current if i know power in MW and voltage 11kv/415v and also want to know that incoming cables for trnsformer

6 Answers   Daikin, KOC, Reliance,


How conventional fire alarm system works?

1 Answers  


what is advertised hop count

0 Answers  


what is advantage of using star to delta in place of dol starter

4 Answers  


What should be the Sandwitch type Al. bus bar capacity for 2 M.W.Gen. set, having continuous full load current- 3463 Amps,ambient temp.- 50 Deg. C., Required temp. raise-20 deg.C., it will run 24 hrs, 365 days on full load, required highly reliable.

0 Answers  


Why the pointer of earthing of 3 pin top is made thick and long compared to the phase and neutral pin ?

3 Answers   Sanima Hydro Power,


can we use inductor for passing or blocking of AC or DC?

3 Answers   Moser Baer, NTPC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)