HOW TO SIZE THE TRANSFORMER OR WHAT ARE THE STEPS INVOLVED IN
FINDING THE SIZE OF THE TRANSFORMER FOR GIVEN LOAD SAY 2000KW
?
cosq = kw/kva
for 2000kw
cos q *kva
suppose
cosq=.85
2000/.85 =2352.9412
so we need 2500kva transformer...
| Is This Answer Correct ? | 5 Yes | 0 No |
is it value of power factor is more than unit. whats effects in the source supply
In the diesel generator if there is an AVR (auto voltage regulator) gone faulty, in this condition is there any way to generate the voltage from the alternator? I need a brief explanation can you please help somebody
High voltage test procedure of in swgr board. why should measure millivolt drop on testing time?
what is the natural resistance of the earth? and how it effected by rain r snow? wat is the natural resistance of wet soil? define natural resistance?
Why we find the sensitivity for the CT's to check?
what is the diffrence between voltage and current?
which power plant has high load factor?
Difference between mcband isolator
Hi, what is 100 % stator earth fault protection and how it can be achieve by 3rd harmonics and low frequency injection principle ?
What is Ton Capacity of Air Conditioner?
Why power factor should not be in leading (capacitive) mode of any load.
why is the size of earth conductor is half of phase conductor.
1 Answers Century Pulp and Paper, L&T,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)