Answer / sundar m
According to the P-f Q-v the reactive power supplied by the
machine will be depends on the excitation voltage so by
varying the excitation voltage without affecting the
synchronization of alternator we can vary the powerfactor of
the machine
| Is This Answer Correct ? | 1 Yes | 0 No |
Why the power generated in dams is complex power? Why the generators in dams cannot produce Real power directly (i.e power which has zero reactive part)?
What are m circles?
What is the black star?
if we convert watt into kva,which one formula use by us,pls tell me?
How to calculate KVA/VA rating of PT or CT from primary & secondary voltage or primary & secondary current?
in catridge heeter watts =110, 260 v , i checked in multimeeter meeter shows 50 ohms but oms law r=v square /w 260*260=67600, and 67600/110=614.5 ohms how to caluclate exact ohms in heetre s
in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv, it operate or not???
Why is the starting current high in dc motor?
Explain RLC circuit?
what is the main purpose of line PT and bus PT?
How to calculate cable size by using load.?? Any formula...
3-PHASE 15KVA dg IS EQUIVALENT TO 12 KW,hOW?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)