for which possible reasons a motor can fail to start??
Answers were Sorted based on User's Feedback
Answer / sathiyakeerthi
The power is not there
check the I/P & O/P wire
Check the Starter
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / sheleph
we need to check below things if motor not getting started
whether any fault is coming when we start the motor
If not then check
Check voltage healthiness
each stop(LCS,DCS,ECS)should be released
Check wheather any of the BIs of Relay not working
Check interlock as per drawing
if still not happening then check respective contactor or
breaker
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / praveen
when both the field flux and armature flux are opposite then resultant electromagnetic torque going to zero this results such that it does get necessary driving force
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / makwana girish
Starter conection wrong first check afteer motor start.
By Company(L&T)
| Is This Answer Correct ? | 0 Yes | 0 No |
How can you test the vector group of power transformers?
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
can wind-turbine effect on rain or on cloud's
What happen if you keep open the Neutral Grounding Switch in open condition of the HT Generator at starting and again on load if it open then?
where is the primary of CT??
why diesel tank is earthed
if there are six generators (3 gas CATT, one Jenbacher o1 MW each, and two nos Diesel 01 no 01 mw other 0.65mw EDGs ( say), 3 CAtt gas set have identical pole pitch,01mw EDG and Jenbacher gas Set have different pole pitch, how their power connection can be done to connect a common bus bar during installation. in short, how different pole pitched generators power connection can be done to connect a common busbar system through generators incomer ACBs.
WHY MOSTLY Rph IS USED FOR CONTROL CIRCUITS AUX. SUPPLY ?
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
examples of resistive inductive and capacitive load
what is the principal of star delta starter?
whow we find out dc motor field aur armature resistance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)