for which possible reasons a motor can fail to start??
Answers were Sorted based on User's Feedback
Answer / sathiyakeerthi
The power is not there
check the I/P & O/P wire
Check the Starter
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / sheleph
we need to check below things if motor not getting started
whether any fault is coming when we start the motor
If not then check
Check voltage healthiness
each stop(LCS,DCS,ECS)should be released
Check wheather any of the BIs of Relay not working
Check interlock as per drawing
if still not happening then check respective contactor or
breaker
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / praveen
when both the field flux and armature flux are opposite then resultant electromagnetic torque going to zero this results such that it does get necessary driving force
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / makwana girish
Starter conection wrong first check afteer motor start.
By Company(L&T)
Is This Answer Correct ? | 0 Yes | 0 No |
What is difference between incomer & outgoing type Vaccum Circuit Breaker?
determine two methods to find loose connection in operational electrical system?
how to increase senstivity of ct
how to find the transformer effiiency
Differentiate between digital phase converter and ordinary phase converter.
CAN CU XLPE/PVC CABLE BE USED INPLACE OF LOW NOISE SCREENED CABLE? KINDLY GIVE REASONS
Which loss in DC machine is maximum?
what is arc flash and what are the hazards involved
what is the spdt
How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test?
What is the function of auadag in a cro?
How calculate cable size & voltage drop for the following requirement connected load 150 KW distance cable length 1000 M voltage 3 phase 415 v.