avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed sajid
I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / it might be for easy calculati
It might be for
easy
calculation:-)
Is This Answer Correct ? | 2 Yes | 3 No |
How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts
How to the calculating the Reactive power ( kvar )
How many types of relay are present in a VCB and ACB, what are the tests we can conduct on both breakers and how to set the relays values
HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?
1 Sq.mm ( Aluminium Cable ) = How much Amphere ( AMP )
Why collecting electrode of ESP to be earthed
How much resistance between neutral earthing and body earthing of Power transformer?
Give details of your interested designation, the post you are interested to serve the company better and explain why you think you can serve the company better in such position if employed?
HOW TO WORK A VFD?SAY SIMPLE METHOD
i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.
0 Answers Bay Fishing Corporation,
what is the function of capacitor duty contactor in an capacitor panel???
are you hear the meaning of burden , excat meaning of burden in only one word