avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....

Answers were Sorted based on User's Feedback



avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.

Is This Answer Correct ?    1 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.

Is This Answer Correct ?    1 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / mohammed sajid

I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / balu

Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / k.prakashchandra

It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.

Is This Answer Correct ?    0 Yes 0 No

avr is an automayic voltage regulator ... it regulates voltage before it synchronise with grid a..

Answer / it might be for easy calculati

It might be for
easy
calculation:-)

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

How do you calculate the actual power consumption of an inductive load appliance. Say, a deep freezer of 200watts

0 Answers  


How to the calculating the Reactive power ( kvar )

3 Answers  


How many types of relay are present in a VCB and ACB, what are the tests we can conduct on both breakers and how to set the relays values

2 Answers   Hyundai, Sodexo,


HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?

1 Answers  


1 Sq.mm ( Aluminium Cable ) = How much Amphere ( AMP )

4 Answers   Google, TATA,






Why collecting electrode of ESP to be earthed

0 Answers   NBVL,


How much resistance between neutral earthing and body earthing of Power transformer?

1 Answers  


Give details of your interested designation, the post you are interested to serve the company better and explain why you think you can serve the company better in such position if employed?

0 Answers  


HOW TO WORK A VFD?SAY SIMPLE METHOD

1 Answers   GE,


i need to now what will be the cable size to the following load, transformer to distribution panel distance 110m, load 1000kw, voltage 400v, pf 0.85, permissible voltage drop 2.0%, overhead line, atmospheric temperature 35 degree c.

0 Answers   Bay Fishing Corporation,


what is the function of capacitor duty contactor in an capacitor panel???

0 Answers  


are you hear the meaning of burden , excat meaning of burden in only one word

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)