avr is an automayic voltage regulator ... it regulates
voltage before it synchronise with grid after
synchronisation it regulates power factor why....
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
AVR maintains the set voltage and does not regulate it.APF
mode is an option in Auto- channel in addition to AVR mode
and it is put in action after synchronization.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
After synch,AVR keeps the gen voltage constant at the set
value. If the grid voltage is more than the gen voltage, the
pf becomes leading and lagging if the grid voltage is less
than the gen voltage.Then, in AVR mode the operator has to
reset the gen voltage so that the pf is slightly lagging.In
APF mode ,the pf always remains at the set value
irrespective of variations in grid voltage.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mohammed sajid
I can't understand your language mr.prakash,just explain
what is the function of AVR before & after synchronisation
with grid.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / balu
Once the generator connects with the grid the system voltage depends upon to the grid referrence.the active power varies depends on the load.so load varies mean time reactive power also variey.so avr will maintaine power factor after synchronization.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It is possible to have the changeover from AVR to APF mode
automatically on synchronization / closing unit CB and the
vice versa, using auxiliary switch of the breaker.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
It keeps the gen voltage the same at the set value
irrespective of variation in speed , load and grid voltage
after synchronization. It is useful whenever there is grid
failure as the gen speed suddenly increases to an extent
depending on the load interrupted.Then AVR does not allow
for rise in voltage.It is also very helpful while
synchronizing as you do not have to vary the excitation
every now and then ,once you have matched the voltages.If
you desire to keep the pf constant after synch and loading
,you have to switch over to APF mode from AVR ,both being
available with Auto channel.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / it might be for easy calculati
It might be for
easy
calculation:-)
| Is This Answer Correct ? | 2 Yes | 3 No |
How many types of lightings are there
hi.. i am krishna. i've complide my diploma engg.in electrical.i applied many places for jobs.but i am always fear from written test.ican't get success in it. i think my basic engg. is weak..show me some idea please..!
How to calculate per unit impedance of transformer?
what are the components of a start and stop motor control?
how to calculate the output power of vfd , please help me.
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
State kirchoff current law?
How to test the vector group of a Yd11 transformer? what are the relations to be checked between various vectors to confirm this vector group?
what is mean by current
WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
Why is the uniform distribution of the capacitor discs in a suspension type insulators essential , what can u do to improve the string efficiency ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)