for which possible reasons a motor can fail to start??
Answer Posted / sheleph
we need to check below things if motor not getting started
whether any fault is coming when we start the motor
If not then check
Check voltage healthiness
each stop(LCS,DCS,ECS)should be released
Check wheather any of the BIs of Relay not working
Check interlock as per drawing
if still not happening then check respective contactor or
breaker
| Is This Answer Correct ? | 5 Yes | 0 No |
Post New Answer View All Answers
why electronic instruments is more favorable than electrical?
how we can find of current direction(supply comming/out going direction) when a transmission line passing through sides.
What is formula calculation size cable wire ?
If any cable burnt how can we identify it burnt by high current of high voltage?
How to select HT/MV cable size ?
any one can explain the stages of a knee point which is taken during ct magnetising curve.
When we connect the large capacitor bank in series ?
What is the unit audit? if our Max demand is something and we found much more unit then how to improve our max demand?
What are the factor to be consider for CT selection in 132kV substation?
What are the protections for safe running of electric generator?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
What is the phase relationship between the primary and secondary voltages of a transformer?
What Should be the value of Vector Surge angle at Tripping and how to calculate it?
Let me know that how i calculate the alternator sub tranciant reactance and tranciant reactance.
what happen when power factor of 2 parallely operated transformer become equle?