IF we have 500kva transformer 11.0/0.415V, 50Hz. How to
calculate the current on HT & LT side, how can we consider
for its breaker (HT & LT both)? You are requested to solve
the question herewith.
Answers were Sorted based on User's Feedback
Answer / antaratara ghosh
current on HV side= 500/(1.732*11)
= 26.24 A
current on LV side= 500/(1.732*0.415)
= 695.6 A
Breaker on HV side will be 630 A VCB (since it is the
lowest available VCB and in HV side you have to go for
VCB/SF6)
Breaker on LV side will be =greater than (1.2*695.6)A i.e.
834.72 A
so we consider it to be 1000 A ACB
| Is This Answer Correct ? | 19 Yes | 3 No |
Answer / a.i.a
As, usually the ultimate load current for any distribution system take 20% spare loads for future , so full load current shall be multiplied by 0.2 more (i.e 1.2) to calculated MCCB rating.
hope you got the correct answer.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why water bubbles when D.C. Current is passed through it? Why not when A.C. Current is passed?
TNC switch is also available in 1NO+1NC. What does it mean ?
Why P.F(power factor)relay should not be connected to the D.G(diesel generator) incomer side
if the back emf eqution for dc motor EB=(QPNZ/60A) THEN what is the value of A for PMDC MOTOR OR how can dicide the value of "A"
the transient state stability limit of a system wherin power is transmitted throgh a double transmission line is (a)equal to steady state stability limit (b)more than its steady state stability limit (c)less than than its steady state stability limit (d)equal to its dynamic stability limit
After synchronization with grid how to maintain the power factor in lagging or in leading? if lead of lag what is the problem?
power generation unit kw/hr or kw/day ?? please answer me engr_kalam@yahoo.com
In what cases (circumstances)we should apply P controller, PD controller, PI controller & PID controller ?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage. note--it is tested with 5000 kv megger and insulation resistance is 0.05 M ohm. and some time 0.03 M ohm comes.
to operate air conditioner of 1.5ton what power of generator is required
why cannot we use a freuency more than 400hz is used in aircrafts?
difference between synchronous reluctance motor and switched reluctance motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)