725KW Three DG set Synchronised but DG no-1 power showing
750KW DG n0-2 power showing 500KW DG no-03 showing 500KW.
DG is Shynchronised but why this different power showing?
Answers were Sorted based on User's Feedback
Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
| Is This Answer Correct ? | 2 Yes | 2 No |
What happen if 200KVAR capacitor continuesly connected to load and all the plant machinaries are not in working?
How to calculate mf when meter equipment and meter are connected
Why NGR is required for 11Kv geneartor in power plant
Hi, Next week Iam appearing RRB exam for section engineer. So help me to get modal question papers for this position. Iam very thankful to you. Whether question will be fully techanical format or general form. Please give me a details regarding this exam.
In A.C systems, fuse is placed in phase-in order to disconnect the circuit during faulty condition. But, what is the reason for putting "LINK" in neutral istead of connecting through (same) wire.
Whats changes in Transformer Oil BDV in changes in temp or Climate?
Is earthing done for AC or DC or both?
What is the suitable rating of MCB used for 1.5 Ton A.C & why?
what are clipper and clamper circuits?
What is the unit of charge and current?
what is the transformer
What is the function of Harmonics filter, and how to calculate that rating of the energy saving?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)