725KW Three DG set Synchronised but DG no-1 power showing
750KW DG n0-2 power showing 500KW DG no-03 showing 500KW.
DG is Shynchronised but why this different power showing?
Answers were Sorted based on User's Feedback
Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
Is This Answer Correct ? | 2 Yes | 2 No |
WHY L-G FAULT IS MORE SEVERE IN TERMS OF RRRV?
0 Answers Engineers India Limited,
What is BusBar integrity test and how it is conducted?
What happened when we give 2 phase supply to a 1 phase equimpent. It's effect on equipment's efficiency and life?
What are the types of control system?
what is buscoupler adopter panel????
how to define tell me about self
When do you use a VFD motor?
ful form of gis
how can H.V busbar in a powerstation can be protected?
If a 3 phase transformer is a 500 kva using the formulae 500kva= 500000/433 x 1.732 = 666.71amps does this mean that each phase on the secondary side is 666.71
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
why vaccum circuit breakers are preferred over m.o.c.b