725KW Three DG set Synchronised but DG no-1 power showing
750KW DG n0-2 power showing 500KW DG no-03 showing 500KW.
DG is Shynchronised but why this different power showing?
Answers were Sorted based on User's Feedback
Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
| Is This Answer Correct ? | 2 Yes | 2 No |
how can we can take BDV test in transformer?
what is dry and wet frequency withstand voltage? why & where it is used??
What is difference between Electrical & Electronic Device?
7 Answers AZ Engineering, Vodafone,
what is the write prosidure of stringing of 8meter pcc pole.
A resistance of 50 kΩ has a conductance of:(a) 20S(b) 0.02S(c) 0.02 mS(d) 20 kS
how does PLCC work?...
Readings of ER300P Trivector meter
In case of motor Power Factor Generally We Apply A Capacitor But How Can We Know That A Motor is Running On Very low Power Factor And What Rating Of Capacitor We Have To Place And Tell Me Conversion Of Micro Farad to KVAR>
What is turbocharger in a generator?
what is the difference between ground and neutral?
what will be happened when a single phase motor is supplied by the dc supply
wish of these transformer uses oil?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)