Answer / jince
Regarding paralleling DG sets we sticks only on the theoratical conditions of same voltage frequency phase angle and phase sequence. And now a days its easy to achieve using sync relays. Load sharing is the major thing in paralleling the DG sets. Many factors are depending on it
1. Droop of individual DG set must be same
Droop implies both voltage and frequency droop. it is the percentage of noload voltage or frequency. ex. 1% 2% 3% etc. Ex.1% voltage droop of 420V(noload)is 4.2V and it means on full load DG voltage comes down to 415.8V and not any more
Same is the case with frequency droop. All DG's droop must be same
2. On loadsharing we adjust voltage of DG's to met REACTIVE POWER AND SPEED(FREQUENCY) TO SHARE ACTIVE POWER
In order to share the load evenly we must control the voltage and frequency of individual DG's constantly
And it depends on load nature
In my personal experience for resistive loads (lamps)
loadsharing is not required as no variation occurs
For varying loads like lifts motors ac chillers compressssors etc constant loiadsharing is required
For clarification please reply
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tango
synchronization is basically done with Voltage, Frequency and Phase angle but It is recommended to Have same Power Rating of Transformer or DG, in your case it seems to be using DG's of Different rating and so they have been showing Power as per their capacity
| Is This Answer Correct ? | 2 Yes | 2 No |
what is apparant power and reactive power
what type of earthing do for dry fissure rock?
how to extend relay operating timing in 24V dc relay card (without using Timer )
what is the difference between STAR and DELTA connection and application wise how it can be utilizedd ???
what is rated current and operating current?
How many types of faults are there in 3 phase power system?
what is difference between electrical and electronics
when is safety goggles use mandatory?
What is phase in electrical engineering?
Why rotating machines are not allowed to run near critical speed region?
What will be the total current for 300kva UPS if it runs on 40 to 45 percent load. Is there any formula for to calculate the exact load.
how the testing of CT OF 400/200/100 done in33/11 kv s/s
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)