Why the Transformer connection is changing in different
transformer?(Like Star & Delta,Delta & Delta,Star &
Star,Delta Star)
From that connection where it is used?
Answers were Sorted based on User's Feedback
Answer / j.b.
(1) in the star - star connection 57.7% of the line voltage
is impressed upon each winding, but full line current flows
in each winding. power cicruits supplied from a star -star
bank often create serious distrubance in communication
circuits in their vicinity. It is seldom used.
(2) The Delta Delta connction is often used for moderate
voltages. An advantage of this connection is that if one
transformer gets damaged or if removed from service,the
remaining two can be operated in open delta or V-V
connection, but the capacity of the bank is reduced to
57.7% of what it was with all threee phase are in working.
(3)The Star Delta connction is suitable for step down a
high voltage. In this case, the primary is designed for
57.7% of the high tension lines.
(4) Delta Star connction is commonly used to step the high
voltage.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / prashant
Caz, Dependiblity of load sharing transformer which is
using in strarting load consider .
Is This Answer Correct ? | 2 Yes | 0 No |
what is transformer tap change HT side and LT side
How many earthing pits are requier to disapper the surge current of one lighting arrester.
How to reduce current flowing in neutral due to unbalanced load conditions in a three phase system.
how to convert psi into kilo pascal? what is the suction pressure & discharge pressure of chiller?
a new 3ph induction motor doesn't rotates their ratted speed, why ?
Main Differance between Primary Distribution & Secondary Distribution Of Electricity....?
WE know that for Inductor X=2pifL,In DC f=0,then X=0 so,V=IX=0;But In the DC excitation of rotor of AC generator,DC motor field coil which coils are inductor so why does not applying DC voltage short the rotor coil of AC generator and field coil of motor?If it would then DC source might be damaged but it is not happened. Why does the strand conductor of Electrical power transmission line make twist?
What's mean HVF & HAF in Vacuum Circuit Breaker?
0 Answers Gandhi Institute of Technology and Management (GITAM), Hyundai, Jayam Engineering Works,
How can we calculate the rating of a transformer suppose if load is 1000KW?Formula?
What is the power ratio between power in Star and Delta circuit?
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
Why generator field rheostat is set to maximum position and motor field rheostat is set to minimum?
5 Answers Bhel, College School Exams Tests, TCS, Texas,