Why the Transformer connection is changing in different
transformer?(Like Star & Delta,Delta & Delta,Star &
Star,Delta Star)
From that connection where it is used?
Answers were Sorted based on User's Feedback
Answer / j.b.
(1) in the star - star connection 57.7% of the line voltage
is impressed upon each winding, but full line current flows
in each winding. power cicruits supplied from a star -star
bank often create serious distrubance in communication
circuits in their vicinity. It is seldom used.
(2) The Delta Delta connction is often used for moderate
voltages. An advantage of this connection is that if one
transformer gets damaged or if removed from service,the
remaining two can be operated in open delta or V-V
connection, but the capacity of the bank is reduced to
57.7% of what it was with all threee phase are in working.
(3)The Star Delta connction is suitable for step down a
high voltage. In this case, the primary is designed for
57.7% of the high tension lines.
(4) Delta Star connction is commonly used to step the high
voltage.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / prashant
Caz, Dependiblity of load sharing transformer which is
using in strarting load consider .
| Is This Answer Correct ? | 2 Yes | 0 No |
How one can check the charger of the mobile phone or any other charger .......... that is it working ? if , working is it delivering the required supply which is needed by the battery to charge properly ?
If 11 KV breaker on the primary side of a 11 KV/3.3 KV 12.5 MVA transformer can be installed at a distance of 1000 mtrs through a 11 KV cable. If no what are the probable reasons.
why the transformers are rated in kv not kw?
Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?
can we run all LT motors at 360 volts which are normally rated 415+/-10% voltage rating
1.WHAT ARE TRANSMISSION LINE LOSSES DURING WINTER AND SUMMER SEASON? 2.WHAT ARE THE CAUSES/ 3.WHEN THE CORONA IS MORE?.,WHETHER WINTER OR SUMMER? 4. WHAT IS THE PERCENTAGE OF LOSSES IN TRANSMISSION LINE?
Why mostly GT(Generating Transformer)has only Ynd1 Vector Group?
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
when we gave dc supply to 220v dc motor its rpm is 1200. then we gave 180v. how many rpm of its motor. gave answer with calculation at my ID.... ravizak@ymail.com
What are the disadvantges of leading power factor
what is MEMS and any one of it applications?
If breaker is undefined position, first step to do.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)