Answer / anwar mydeen
Air to open valve: the pneumatic valve will open when the
air is applied in to the actuator chamber. and the valve
will goes to close condition when u remove the pneumatic air.
In oil industry oil outlet and produced water outlet control
valves are air to open valves.
Air to Close: the pneumatic valve will close when the air is
applied in to the actuator chamber and the valve will goes
to open condition when u remove the pneumatic air.
| Is This Answer Correct ? | 63 Yes | 5 No |
Answer / mohammed abdul rahman
This query is mostly related to pneumatic diaphragm actuated control valves. Air to open valves have the pneumatic input on the under-side of the diaphragm with a spring on the topside, which causes the valve to open on increase in control signal. Air to close valves will have the pneumatic input on the topside of the diaphragm with a spring on the under-side to provide counter force.
An i/p converter will convert the 4-20mA signal from control system to an equivalent 3-15psi pneumatic signal to actuate the control valve.
A positioner will have the i/p converter inbuilt and is connected to the moving part of the valve and automatically adjusts the signal to the actuator to maintain a position proportional to the signal. This introduces a loop inside a loop.
Please refer the control valve handbook from Fisher for reference. It is available as a free download.
| Is This Answer Correct ? | 37 Yes | 4 No |
In a class of 150 students, 40 passed in Social Studies, 90 passed in Science and 30 failed in both the subjects. vi)How many students passed in at most one subject among Science and Social Science?
7 Answers CAT, CGI, Cipla, KHK, Visa,
Where are oxygen analysers installed in cfbc boilers? What are their usual readings?
hw to calibration a control valve?
a laways iface problem with brine level transmitter sealing diaphram a laways giving error and maximum reading i made re range and adjust with side glass but during commission it giving gap reading between it and side glass i need help from expert to explain how to calibrate it. note:dp transmitter yokogawa company
why do we use 4-20mA as o/p and why don't use 0-20mA or 5- 21mA?
What pressure results for a flow transmitter of range 0- 180t/h in the dcs and 0-301mbar in the field using square root extraction. Kindly also suggest formulae for the percentages 0,25,50,75,100?
Where should we terminate the shield and why?
What is NAMUR standard and why its allways reletad with Sollenoid
what is the difference between PLC & DCS
what is diff b/w neutron and ground?
how does we do bench calibration of a differential transmitter.
What is scale factor of proximitor & unit of the viabration.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)