There is a problem with our HART475 it is not communicating
with smart devices error becomes "NO DEVICE FOUND"we have
insert 250ohm resistance as per requirement but invain plz
tell me the solution?
1) How do you know that the device talks HART? Many field transmitters talk Brain, Honeywell DE, Foundation Fieldbus, Profibus or 4-20mA only.
Have you confirmed the HART functionality on that device?
2) Point-to-point (communicator-to-transmitter) is usually done with the device at address 0 and with the communicator polling address 0.
Is the communicator polling address 0?
Is the device at address 0?
3) On many transmitters, HART can be disabled. Is HART enabled on this transmitter?
4) The transmitter has to be powered, initialized and in its operating mode in order to communicate via HART. Sometimes transmitters are not powered, but when connecting from the a marshalling panel, it is obvious, because the transmitter is remote location. Is the transmitter powered and operating?
5) Are connections across the dropping resistor or across the transmitter's (+) or (-) terminals? Connecting across a pressure transmitter's 'test' terminals will not work properly for HART communication.
6) A loop isolator module that is not specifically designed for HART will strip off the HART signal, but pass the 4-20mA current signal. If a loop isolator is installed in the loop, is it designed for HART operation.
7) If the power supply ripple and noise exceeds the HART specification, the power supply noise will interfere with HART or prevent communication entirely.
8) The 475 can have 3 terminals at the top where the banana plug field cable plugs in. 2 terminals are for HART, 2 terminals are for Foundation Fieldbus (FF). If the cable is plugged into the 2 terminals for FF, HART communications will be blocked by not having a cable in the correct port.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the difference between two wire transmitter and 4- wire transmitter
what would be the minimum flow rate that we can measure on rotameter..?
What is expansion of SMART Instruments? And What is it?
what is PID n give me brief info. about P&I&D.
what is piezo electric transducer?its principle?
Can any body help me,The GE Mark V control system is windows based or Dos based?
can anyone tel the syllabus or previous year question paper for BHAVINI(EIE)2014.
Why humidity limit is 30 to 55 % for raw material storage?
How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808
1.what is beta in control valves? 2.what is the condition followed by light in LASERs? 3.1kg/cm2=?psi 4.Integral action reduces what? 5.about vena contracta 6.a simple RC circuit 7.thermistor material's temp coefficient of resistance 8.if wave passes through the thicker area of a chord to a thinner area what changes will occur to wavelength? 9.if 4-20 mA represents 0-10 kg/cm2 what will be the current when pressure is 5 kg/cm2.................
What is megering????
hw to calibration a control valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)