Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


There is a problem with our HART475 it is not communicating
with smart devices error becomes "NO DEVICE FOUND"we have
insert 250ohm resistance as per requirement but invain plz
tell me the solution?



There is a problem with our HART475 it is not communicating with smart devices error becomes "..

Answer / carl_ellis

1) How do you know that the device talks HART? Many field transmitters talk Brain, Honeywell DE, Foundation Fieldbus, Profibus or 4-20mA only.

Have you confirmed the HART functionality on that device?

2) Point-to-point (communicator-to-transmitter) is usually done with the device at address 0 and with the communicator polling address 0.
Is the communicator polling address 0?
Is the device at address 0?

3) On many transmitters, HART can be disabled. Is HART enabled on this transmitter?

4) The transmitter has to be powered, initialized and in its operating mode in order to communicate via HART. Sometimes transmitters are not powered, but when connecting from the a marshalling panel, it is obvious, because the transmitter is remote location. Is the transmitter powered and operating?

5) Are connections across the dropping resistor or across the transmitter's (+) or (-) terminals? Connecting across a pressure transmitter's 'test' terminals will not work properly for HART communication.

6) A loop isolator module that is not specifically designed for HART will strip off the HART signal, but pass the 4-20mA current signal. If a loop isolator is installed in the loop, is it designed for HART operation.

7) If the power supply ripple and noise exceeds the HART specification, the power supply noise will interfere with HART or prevent communication entirely.

8) The 475 can have 3 terminals at the top where the banana plug field cable plugs in. 2 terminals are for HART, 2 terminals are for Foundation Fieldbus (FF). If the cable is plugged into the 2 terminals for FF, HART communications will be blocked by not having a cable in the correct port.

Carl Ellis
Measure First

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

pls tell me whethere flame proof HMI's are available or every HMI is manufactured by considering flame proof standard.

3 Answers  


how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.

0 Answers  


What is the difference between EPROM & EEPROM.

1 Answers   Sabic,


Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?

3 Answers  


can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............

2 Answers   Asec, Honeywell,


What s PDS & PDMS tools ?its role in instrumentation?

1 Answers  


How a rtd work, and what volts/current goes to a RTD to measure the resistence?

1 Answers   DVC,


in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?

0 Answers   IOCL, JSW,


what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.

0 Answers   Sabic, Saudi Aramco Shell Refinery Company SASREF,


What are securities of turbine?

1 Answers  


What is the use of the shield wire and how is the connection at both the ends of a shield wire?

2 Answers   Samsung,


what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC

1 Answers   Bharat Biotech, TATA,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)