There is a problem with our HART475 it is not communicating
with smart devices error becomes "NO DEVICE FOUND"we have
insert 250ohm resistance as per requirement but invain plz
tell me the solution?
1) How do you know that the device talks HART? Many field transmitters talk Brain, Honeywell DE, Foundation Fieldbus, Profibus or 4-20mA only.
Have you confirmed the HART functionality on that device?
2) Point-to-point (communicator-to-transmitter) is usually done with the device at address 0 and with the communicator polling address 0.
Is the communicator polling address 0?
Is the device at address 0?
3) On many transmitters, HART can be disabled. Is HART enabled on this transmitter?
4) The transmitter has to be powered, initialized and in its operating mode in order to communicate via HART. Sometimes transmitters are not powered, but when connecting from the a marshalling panel, it is obvious, because the transmitter is remote location. Is the transmitter powered and operating?
5) Are connections across the dropping resistor or across the transmitter's (+) or (-) terminals? Connecting across a pressure transmitter's 'test' terminals will not work properly for HART communication.
6) A loop isolator module that is not specifically designed for HART will strip off the HART signal, but pass the 4-20mA current signal. If a loop isolator is installed in the loop, is it designed for HART operation.
7) If the power supply ripple and noise exceeds the HART specification, the power supply noise will interfere with HART or prevent communication entirely.
8) The 475 can have 3 terminals at the top where the banana plug field cable plugs in. 2 terminals are for HART, 2 terminals are for Foundation Fieldbus (FF). If the cable is plugged into the 2 terminals for FF, HART communications will be blocked by not having a cable in the correct port.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what is the control valve?how many types of control valves are there
6 Answers Chemin, Hindustan Zinc,
I am manjunath having exp in maintenance of chemical plants,know i want to do a design course INTOOLS,after doing design course can we get jobs in design field.sinve i dont have design exp..
Why are the uses 24vdc in industries
If we increase PI controller what will be action.
in my company organisation in plan to take new PLC system for replacing old relay system , for that what I/P needsd to submit to the system house of PLC supplier?
What is standard procedure of manual mapping in Radar type level transmitter?
how to calibrate motorized operated valve?
1 Answers Bilt, Jubilant, SRF,
what is the procedure of O2 sensor(ABB) calibration?
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
Name different parts of a pressure gauge.
If a transmitter is installed 10 m below its tapping point how much pressure exerted if fluid is water?
what is difference between wheatstone bridge, pirani gauge and strain gauge ??? explain its principle and working
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)