hw to calibration a control valve?..

Answer / aftab ahmed mazari

Following procedure should be done for control valve
calibration.
Suppose it is spring loaded and direct action.(Direct
action means at top of diapgargm signal and with the
increase of signal, stem will move downwards or the stem
will extend).Also valve is signal to close. Check its Bench
Set. Suppose it is 6 to 21 PSI.
1. Set pressure regulator of positioner at about 30 PSI.
2. Apply 3 PSI (4 mA if positioner is smart or electronics)
signal to Positioner.Gradullay increase signal. Note the
movement of stem.
3. Apply 6 (8 mA),9 PSI (12 mA), 12 PSI (16 mA) and 15 PSI
(20 mA) signal. Valve stem should move accordingly and
indicator must show 25%,50%,75% and 100%.
4. If error, remove it from zero and span of positioner.
5. If facing any error problem, give signal 50% and then
remove error. Rest will be ok automatically.
6. Suppose valve is normally closed and at any vent service
and signal to close as I mentioned earlier, then make shut
close of valve at 14.5, or 14.7 PSI. Valve may start
closing at 2.75PSI.
7. If valve is at control operation, like level, pressure
etc, then calibrate it accurately.No need to calibrate it
at 2.75 and 14.5 PSI.
aftabmazari@yahoo.com

Is This Answer Correct ?    31 Yes 3 No

hw to calibration a control valve?..

Answer / r.murugan

IF ITS PNEUMATIC CONTROL VALVE FIRST WE HAVE TO CHECK
INSTRUMENT AIR PRESSURE THEN WE HAVE TO REGULATE THE
INSTRUMENT AIR PRESSURE REGULATOR TO I/P COVERTER AND
PNEUMATIC POSITIONER
BEFORE STROKING THE VALVE WE HAVE TO CHECK VALVE AT NEUTRAL
POSITION IF NEUTRAL POSITION THEN ONLY CAN MOVE THE THE
VALVE
IF AIR TO OPEN VALVE WHEN COMMAND 4ma VALVE POSITION SHOULD
BE CLOSE (DIRECT OPERATION) LOCAL WE HAVE TO MECHANICAL
SCALE CLOSE INDICATION
THEN INCREASE THE CURRENT 4.5ma TO 5ma to check the start
of opening the control valve
then gradually can increase and decrese the current and
corrospondingly check the stroke momemnt based on command
we have to check the feedback

Is This Answer Correct ?    16 Yes 7 No

hw to calibration a control valve?..

Answer / sajid ali khan

In addition to the Calibration, it is also crucial that the
Control Valve (CV) response matches the demands of the
controller.
Normally, the CV is calibrated and checked as already
mentioned in this post, but please appreciate that in real
operation, for most of the time the controller output will
change in very minor amount to counteract the process
upsets or set point changes and the CV need to respond
rapidly and effectively to those changes. Thus if you
observe any CV, or note its trend from the Control System,
you will see movements in fractions of mA/psi etc. Very few
CVs will go to the full close position and valve going to
the full open position is even rarer.
Also, it is necessary that the CV overcomes any stiction,
has minimum hysteresis as well as little dead band.
Therefore, it is important the valve be checked for minor
changes.
How to check that:
1. Move the valve to any position other than at its
extremes, somewhere in the middle.
2. Find a safe spot on the CV stem where you can feel the
minor CV movement against a fixed part of the CV Body. Put
your finger firmly on that spot of the CV Stem. I
repeat “SAFE SPOT,” otherwise if the CV operates suddenly
your finger may be injured.
3. If the CV has a digital positioned with a feedback, the
observation may be simpler and finger feeling may even be
not necessary at all.
4. Now closely observe the CV input signal, preferably the
pneumatic signal on a 6 inch dia pressure gauge of at least
0.5 % accuracy. If digital pressure indicator of similar or
better accuracy is used that would be better.
5. While applying input signal move the CV a small amount,
then apply reverse signal very gently and slowly, and feel
the CV stem movement with your finger, the stem should
move. The numerical value of the input signal against the
minor can be noted from the factory test data of the valve.
In case that is not available it would be known by
experience.
6. Repeat this exercise at two or different CV openings and
always check in forward and reverse directions, till you
are confident of the CV performance.
7. In case valve sticks, shows excessive dead band etc,
then loosening of the stem packing or even CV opening for
inspection to check stem/plug misalignment, or hardened
stem packing may be the culprit.
Regards,
Sajid Ali Khan
engineersajid52@gmail.com

Is This Answer Correct ?    7 Yes 5 No

Post New Answer



More Instrumentation Interview Questions

1.In which princeple DP transmeter works? 2.Why UPS system is use for DCS? 3.How drum lvel controller works? 4.What is the difference between glob valve and gate valve? 5.How axial shift probe work & in which princeple it works?

1 Answers   Luberef, Qatar Gas, Reliance,


Difference between dcs and plc including date processing and architecture.

0 Answers  


Can anybody tell me the exact explanation for Functional calibration?When it should be done on process or on lab? Advanced Thanks

2 Answers  


Please tell me details about Sox,Nox,SWAS analyser????

0 Answers   Essar,


please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com

0 Answers  






what is the difference between sinking and sourcing inputs and also what are there applications?

2 Answers  


what is cavitation in control valve? & how we can avoid it?

1 Answers   Forbes Marshall, Reliance,


why use on -off control valve in glove valve

1 Answers  


what is mean by loop checking?

8 Answers  


How to consider the flow directions for control valve (Globe) Is the there any easy understanding in order to select the flow directions?

3 Answers  


how to calculate flow range in DP tx

1 Answers   Karnataka Power,


GWR radar transmitter working principle?

0 Answers   Tata Steel Limited,






Categories
  • Civil Engineering Interview Questions Civil Engineering (5076)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4445)
  • Electrical Engineering Interview Questions Electrical Engineering (16606)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2992)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1378)