why can't we increase the voltage by increasing the field
voltage in order to get higher voltage.so that we can
eliminate step up transformer
Answers were Sorted based on User's Feedback
i think that, if we increase the field voltage from certain
limit then there will be a chance of sarturation in the
machines.
| Is This Answer Correct ? | 11 Yes | 1 No |
Answer / subrata
I think there are two reasons..
1. Above a certain limit there is a chance of saturation.
2. We will not be able to provide suitable insulation in a rotating machine above a certain voltage.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / waqar ahmad
Every machine is designed for specific insulation level
against voltage level. So increasing voltage, insulation
can get puncture & as a result machine will get failure. so
voltage can't be increased from predefined / designed lavel.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / surendra
In which mode machine is running ,that basiclly tends to
decide the field excitation....apart from this if you
increse the fild excitation to high value saturation
occurs... losses will be more.....
| Is This Answer Correct ? | 0 Yes | 0 No |
what is a starter ??
For polarity test on a 11/3.3kV 2.5MVA delta-star Unit Auxiliary transformer,415V 3-phase supply was applied at the HV. Connection between Aa was made with a 2.5mm cable. As soon as power was switched on the cable caught fire and burnt. This test was then abandoned. It is noteworthy to say that a similar cable was also used in a similar transformer for the same. The cable did not burn and test was successfully completed with good result. What is wrong? Please, help me out.
. The string effcy in AC sys is 80% Then for same power, the string effcy in dc sys is a) less than 80% b) 80% c) more than 80% d) zero
1 Answers Engineers India Limited,
In a 3 phase 4-wire system. For a 3.5 core cable if all loads are single phase and balanced, what will be neutral current? will it be sum of all phase currents? Or it will be zero? And if loads are unbalanced what will be neutral current?
How to decide no. of Step and Kvar for APFC Panel 40 kvar MD: 33.12 KVA Avg pf : 0.8540
low voltage distribution is done by a)3 phase 3 wire b)3 phase 4 wire c)single phase
1ampear me kitna watts hota hai aur elcb ka pura naam kya hai
18 Answers Al Khayyat, Alpha G, BEC, Bhel, CGS, Electrical, Fiem, Firmenich, HLG Habtoor Leighton Group, Jash, Kandia, Maruti Suzuki, Minda, NTPC, ONEIC, Pace Process Controls, SMTC, SR, Sunrise Electrical, Sushil Enterprises, Suzlon, Voltage,
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
what is reactive poower
ohms law aplicable
what is mathed of check the D.C MOTOR 181 KW (ARMATURE AND FIELD) WHAT IS THE MATHED OF CHECK THE THYRISTOR MODULE (HIGH CURRENT)
how define the torque in ac drive. from electrical side in the drive friquency ,voltage and current three factor is there.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)