why can't we increase the voltage by increasing the field
voltage in order to get higher voltage.so that we can
eliminate step up transformer
Answers were Sorted based on User's Feedback
i think that, if we increase the field voltage from certain
limit then there will be a chance of sarturation in the
machines.
Is This Answer Correct ? | 11 Yes | 1 No |
Answer / subrata
I think there are two reasons..
1. Above a certain limit there is a chance of saturation.
2. We will not be able to provide suitable insulation in a rotating machine above a certain voltage.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / waqar ahmad
Every machine is designed for specific insulation level
against voltage level. So increasing voltage, insulation
can get puncture & as a result machine will get failure. so
voltage can't be increased from predefined / designed lavel.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / surendra
In which mode machine is running ,that basiclly tends to
decide the field excitation....apart from this if you
increse the fild excitation to high value saturation
occurs... losses will be more.....
Is This Answer Correct ? | 0 Yes | 0 No |
How they LT panel busbar size choose
how the reverse power relay acts..
In an panel board if the outgoings are power plugs and motor equipments...what should we choose as the incomer of the of the panel board?? MCCB OR ISOLATOR?? Should we use ELCB protection??if so where??
at what basis/standard we have to arrive the current density of aluminium/ copper in busbar?
It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.
what is the meaning of ceiling voltage in Generator exciter?
defination of loads
is the electrical energy photo copy possible or not???????????? give me some idea about that i m very great full tu u.
Dear Friends, I have a 500KVA transformer supplying whole factory having 3 phase and single phase mixed loads. Power room has ammeters connected via CTs for individual phase. Now I know that readings shown on meter for each phase say R,Y and B are line currents. But when I want to know the total on transformer do I need to add the currents of all three phases readings shown on meter or value for anyone phase will give me the correct power load on transformer for that point of time. 2. If ammeter shows unbalanced readings for R,Y, B phases say 150, 250 and 300 respectively so can I assume that 150A i.e average of 3 will be the 3phase load currents and remaining will be 1phase currents. Please clarify my doubt.
all details of DG UPS HVAC
Does VT metering core can be used for synchronizing.
1 Answers Shrishti Power Technologies,
3 ph motor connected in star delta starter. when we start the motor it run in star but when in is going in delta it trips the main incoming supply. why?