Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????

Answer Posted / k.prakashchandra

The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

WHY EARTHING NOT NEEDED IN BATTERY IN SUBSTATION

1958


what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?

2083


When we need up only in o/p 440v, so why we use directly in 11kva in input?

1680


How can we find out LT UG cable fault (size,from-4*25mm sqr to 4*300mm sqr)? How mani types UG cable faults?

3048


What is resonant peak?

1097


What kinds of decision are made about CT from it's Knee point(voltage & current)?

5060


what is current check gurd relay?

2591


Any Electrical Engineering jobs?Please refer for interviews. Thank you

1916


What is distance between electrical panel to land ?

1527


Alternator rotor earth fault relay circuit

2065


the problem faced on star or delta winding connection??

1914


Different STANDARDS (BS, IS, IEC etc) gives different informations on CT specification. How they correspons w r t each other (i.e I mean to say BS provides "knee point voltage" but IS does not, then how can i select CT)

1963


what are the industrail measures to over ferranti effect? how would the ferranti effect the power system if those remedial mearsure arent taken? how often does this effect occurs in real power system?

2137


in indoor type circuit breakers why only the corner breaker trips specially during cold season. What is the reason.

1869


what clearance required for 4.5 mva dry type transformer?

2020