Answer Posted / saravananp
Plate earthing provids using copper plate (450mm x 450mm x
6mm). The area of the copper plate is high causing high
earthing value (Low resistance).
Instaling Method: The copper plate at the depth of 2 Mtr or
3 Mtr. The centre support provides using 40mm GI pipes,
funnel in top.The two numbers of 25mm x 3 mm copper flat
stamped from top of the GI pipe to copper plate to improve
the earth value. The salt, charcole to improve the
conductivity.
The materials using for plate earthing are as below:
1) Meshed Funnel
2) 40 x 300 x 6 mm copper earth pad
3) 25 x 3 Cu strip
4) Copper Rivit
5) 450 x 450 x 3 mm Cu plate
6) 8x25 mm bolt and nut with washer
7) 6x75 mm bolt and nut with washer
8) 40 mm GI pipe - 2.8 mtrs
9) 25mm dia x 200 mm length GI pipe with double end threaded
10) 40mm to 25 mm GI reducer
11) 1" Check nut(6mm thick)
12) Charcoal
13) Salt
14) 450 x 450 mm heavy duty SFRC chamber cover with frame
ersaravananp@gmail.com
Saravanan.P
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
placement paper samples of mspl company
How do we calculate transformer oil in liter from the rating of the transformer.
what is v/f control in VFD?
what is the star delta connetion and how can do it a three phase motor with control witing with picture
What are the components of feedback control system?
iam working in power plant. In hot places tube lights are glowing at the end portion only. what is the reason for that?
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
What are the causes for the failures of sandwich type (Al) busducts?
what is load vs Torque curve & why it is used?
what is meant by loss of field in a DC motor? how a universal motor works?
i want to know that how the height of Ct ,cvt ,LA calculated on the basis of creepage distance
Which device of PlC does share load between DG sets when DG are running in perallel?
Why is back emf used for a DC motor? Highlight its significance.