What is the ideal power factor?
Answer / pradhyumn
Ideal Power factor is 1.
It is ratio of real power(measured in watts) flowing to the
load to apparent power(measured in VA). It ranges between 0
to 1.
P.F. is a measure of the degree to which a given load
matches to that of a pure resistance.
P.F.=1 if load is purely resistive.
P.F.=0 if load is inductive or capacitive or both.
For RL-circuit P.F. is between 0&1.(lagging)
For RC-circuit P.F. is between 0&1.(leading).
Is This Answer Correct ? | 8 Yes | 0 No |
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
what sq.mm copper pvc wire need for ac load current 25amps for 230v ?
What is phase in electrical engineering?
HOW DO I CALCULATE THE SETTINGS FOR THE DIFFERENTIAL PROTECTION OF A 12kV/6.6kV, 6MVA,DYN11 XMER WITH PRIMARY SIDE CTR 400/1 AND SEC SIDE CTR 600/1?
Spacing of Transformers ratings are 10kva,15kva,25kva,63kva,110kva,150kva .........so on Q) Why transformer are not manufactured having ratings in between or other than these standard ratings ?
At a family reunion were the following people: one grandfather, one grandmother, two fathers, two mothers, four children, three grandchildren, one brother, two sisters, two sons, two daughters, one father-in-law, one mother-in-law, and one daughter-in-law. But not as many people attended as it sounds. How many were there ?
Rotor resistance starter is used to obtain= A increased starting torque B decrease starting current C decrease starting loss D increase efficiency
what is sevice settings for mccb?How can be it setted?
Why one side of secondary of transformer is earthed, to supply single conductor of electric traction system?
I WANT YHE TECHNICAL AND ELECTRICAL SPECIFICATIONS OF 2x4MW 11KV 2x10MW 11KV 2x25MW 11KV 2x100MW 11KV HYDEL POWER PLANT i.e PROTECTION SYSTEM,MONITORING,CONTROL SYSTEM,GENERATION,SYNCHRONISATION,METERING PLEASE SEND THE DETAILS TO MY MAIL ID SPRAVEEN_222@YAHOO.CO.IN
how cables go in and come out for distribution from the feeder pillar box?
what size steel armoured cable is required to support 1500kva capacity. would 70mm squared be enough or would I need 90 or 120mm squared 3c plus earth