is any body explain me why return current in three phase
power system is less then in a red, yellow, blue phases???
as we know Ir+Iy+Ib=In then why nutral wire has less then
phase current????
Answers were Sorted based on User's Feedback
Answer / s ray
The vector sum of three phase current is zero i.e neutral current is zero. but deu to load unbalance we get a small neutral current
Is This Answer Correct ? | 47 Yes | 3 No |
Answer / banalasanthosh
whenever a phase is to feed current to nuetral, remaining
two phases also share the current with nuetral.... that
means Ir current flow through yellow , blue and nuetral
also. thata why total current willnot be presented in nuetral
Is This Answer Correct ? | 2 Yes | 0 No |
1 hp single phase motor is more likely to get hot thsn inone hp 3 phase motor its true or false? If true why?
In a distribution system,having 3phases & 1 nuetral.ecah phase to neutral is 230V,line-line voltage is 440V,but what is the voltage of each line.but it should obey the KVL law.
Why does inductive loads consume KVARs?
what are the standard IR values should be of R-E, Y-E, B-E, R-Y, Y-B, B-R of VCB in closed condition and in open condition for 500KVA & 1000KVA transformers. and what is the acceptable range when tested by 5000V megger.
what is LUX?
what is the diff between mcb and vcb
what is the Mechanism of energy saver FAN how average power,reactive power, power factor e.t.c realated to it and how it apply to this FAN .and how this fan save energy w.r.t circuit analysis,plz repaly to this question this is the assignment to given to me.thanks
in industrial lighting in each circuit how many lamps can be given? and how much load can be put on each circuit? is there standard for this? please help me with the standard description?
Can we generate 3 phase power from single phase connections?? If yes, how?
if any body have question paper of railway (section engineering),then plz send me .i will thank of him/her.
what is the difference between the 94 lockout relay and 86 lock out relay. I have noticed that the 94 lockout relay is activated when the distance realy is activated and 86 is activated when the 87T differential is activated. but why can't the same lockouts be used for both the protection schemes
what is the effect of leading power factor on Power transformers in existing in major power utility