In VVVF drive voltage is varying in accordance with
frequency.My question here is How much will be the voltage in
the inverter side if the frquency is set for 10Hz ?
Answer / ramgopal gupta
ans is 46v.i.e v/f should be constant to make air gap flux
constant in the machine.230/50 is 4.6 thats why 46 volts.
| Is This Answer Correct ? | 3 Yes | 0 No |
How to find the maximum load that can supply by a particular(say 315kva) KVA rated transformer?
how many power plants in andhra pradesh,how many types and there capacity
How to calculate the current rating of power cables ?
why the generating voltage in India is 11kV or why is it be transmitted as multiples of 11
34 Answers ACC, Bhel, ECI Engineering and Construction, NTPC, SBL, Senthur Power Services,
why the conservater tank alwes made upper side of transformer???
1.Defination of Graund earth and neutral 2.
What is stray looses?
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
how to calculation increase power factor for single phase
how to calculate differential current when we testing differential relay..suppose we have 1000kw generator,630amp VCB,what value we should put /inject so that relay trip the VCB? PLLZ justify ur comment
how many bulb of 60watt at 300volt is used to maintain 0.25 amp.with valid reason?
what are the reasons of low voltage during start the DG?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)