why neutral and earth should not be connected on 3 phase
440v/50c/s supply at consumer side. where as on
25kv/ac/50c/s railway traction substation neutral and earth
will be connected and track at substation. and track will
act as neutral and earth. Reasons for this is needed
urgently

Answers were Sorted based on User's Feedback



why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where..

Answer / nmr

IF ALL CONSUMERS EARTH ARE CONNECTED TO NEUTRAL AT EACH
CONSUMER POINT, ALL THE EARTH ELECTRODES RESISTANCES ARE
BECOMES PARALLEL ALONG WITH TRANSFORMER SECONDARY NEUTRAL-
EARTH ELECTRODES. HENCE 1/R= 1/R1+1/R2+1/R3+1/R4 ETC.,
THERE EFFECTIVE RESISTANCE IS BECOMES VERY VERY LOW. IF A
30 KVA TRANSFORMER IS THERE. THE CURRENT IL/IPHSE =
30,000/440*1.732 = 40.0 AMPS (WITH UNITY PF) THIS CCURRENT
WILL PASS THROUGH EARTHS ELECTRODES(BECAUSE ALL EARTH
RESISTANCES ARE PARALLEL AND NET RESISTANCE WILL BECOME
LESSER THAN THAT OF NEUTRAL)SO STEP POTNTIAL WILL RAISE
CAUSES ELECTRIC SHOCK TO THE PEOPLE WALKING AT NEAR
TFP/PANNEL BOARDS. IN TRACTION SUBSTATION A EARTH MAT WILL
BE PROVIDED IN THE YARD TO REDUCE THE STEP VOLTAGE NOT TO
GET SHOCK BY THE PEOPLE. OK
NMR/email; bapdada1812@gmail.com electrical engineer

Is This Answer Correct ?    3 Yes 0 No

why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where..

Answer / k.prakashchandra

Consumers earth is for connecting to metal bodies to prevent
shock . The neutral is already earthed at the TC and another
earth means extra expenditure.During earth fault ,there will
be temporary rise in voltage resulting in burning out of
potential coils of the energy meter.And if earth is
connected to neutral wire of supply after the RCCB, it will
trip as a portion of neutral current will be bypassed.

Is This Answer Correct ?    1 Yes 1 No

why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where..

Answer / jicks patel

voltage level at consumer side is generally kept low (230v
or 440v),any shocking moment should face fuse sensually.so
no more cost required like earthing.

Is This Answer Correct ?    1 Yes 2 No

why neutral and earth should not be connected on 3 phase 440v/50c/s supply at consumer side. where..

Answer / shivababa_1812

electrical engineering

Is This Answer Correct ?    1 Yes 12 No

Post New Answer



More Electrical Engineering Interview Questions

How much pole motor can be desion for 415 volt ,50 hz.Power supply. in pratical condition . Prakash veer singh

5 Answers  


I Have 3 Phase 10 KW AC Alternator i found one phase weak, so what will be the reason & what action shouls i take to rectify the same.

0 Answers   Vadilal,


Is corona effect occurs in Induction motor. pl. justify the answer.

4 Answers   KPS,


why Copper loss is represented as I square R ?

5 Answers   L&T,


Hi If connecting a temp generator 670KVA .415kv with step up Tx .415/11kv. I am given Generator impedances Z1 Z2 Z0 to 100MVA base. Do I need to work out the generator fault current by using these impedances i.e gen rating / impedance. Then use this as my source impedance for the calculations that follow.

0 Answers  






why earth hole size is biggest in plug point?

13 Answers   RRB,


what is the significance of 3.5 core cable? or what does this half core mean and why is it required?

5 Answers  


Where there is voltage,there must be current.Is this right or wrong??

10 Answers  


what is meant by poly phase induction motor ? how its operating by single phase or three phase?

0 Answers  


If u have 60KVA UPS, than tell me how systems ( computers ) u may connect?

3 Answers   Thomson Reuters,


What is the permissible sound level for 1000kva DG set and how the sound level is calculated.

1 Answers  


what is the meaning of 5% droop or 7% droop in AVR?

0 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5076)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4445)
  • Electrical Engineering Interview Questions Electrical Engineering (16606)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2992)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1378)