what is the thermocuple compensation circuit

Answers were Sorted based on User's Feedback



what is the thermocuple compensation circuit..

Answer / carl ellis

I disagree with answer #1

>other metals create junction (screw, conducting wire of
another metal)

This does NOT create an error according the Thermocouple Law
of Intermediate Junctions, which states that a 3rd metal
inserted between the two dissimilar metals of T/C junction
will have no effect upon the output voltage as long as the
connection junctions are isothermal, that is, both
connection junctions are at the same temperature.

So compensation is not needed for a 3rd metal because the
error in the positive and negative legs are of opposite
polarity, so the error is self correcting.

There is no practical method of compensating for
non-isothermal conditions so T/C compensation does not refer
to that.

>using ckt that may contain RTD at cold junction, eliminate
known emf at cold junction using electronic ckt

The original question is poorly worded because "thermocouple
compensation" refers to correction of non-linearities of
thermocouple's EMF with respect to the accepted temperature
value. That is done mathematically with a polynomial or in
some cases, with a look-up table, neither of which is an
electronic circuit.

The electronic circuit used with ALL thermocouples is a cold
junction circuit. ALL temperature measurements done with
thermocouples require cold junction compensation. The cold
junction measurement does not 'eliminate' anything, it
provides the required difference between the freezing point
of water and the temperature of the terminal block,
necessary to use standardized tables, all of which are
referenced to the freezing point of water. Without cold
junction compensation, the error of a thermocouple
measurement is the cold junction temperature difference.
That's not uncertainty, that's ERROR.

Industrial applications typically use a thermistor to
measure the temperature of the connection block at the
analog input. That temperature or its EMF equivalent is
'added' to the EMF measurement of the thermocouple.

Cold junction compensation can be done with a 2nd
thermocouple in series inserted into an icebath which still
done for laboratory and high accuracy measurements. A 2nd
T/C qualifies as a circuit, too.

Answer #2 is correct insofar as it refers to cold junction
compensation.

Carl Ellis

Is This Answer Correct ?    4 Yes 0 No

what is the thermocuple compensation circuit..

Answer / yashwant

thermocouple is what an emf generated at junction of two
dissimilar metal. while measuring / recording emf other metals create junction(screw, conducting wire of another metal) emf
will get added to it which is not correct reading. to
eliminate this error we use to compensate error. using ckt
that may contain RTD at cold junction, eliminate known emf at
cold junction using electronic ckt

Is This Answer Correct ?    3 Yes 3 No

what is the thermocuple compensation circuit..

Answer / john peter

compansation cicuit for thermocouple either tempreture
independent metal or electronic element[transistor ckt] to
produce EMF that adding or sutracting from the other end of
thermocouple

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is the difference between sdv and bdv ?

1 Answers  


which are types of orifice tap ?

2 Answers  


What is SLPC & MLPC? How it works?

2 Answers  


Whether the DP transmitter can be utilised in the medium of Vaccum for the measurement of Level?

10 Answers  


I was working on calibrating turbidity transmitters endress+hauser at effluent polishing plant.We calibrated using NTU buffers.What happened is that when we immersed the sensor, everytime we raise and lower the sensor gradually, the reading will vary.my question is that is there any specifications on what is the required distance from the bottom of the container with buffer to the face of the sensor?Is it ok to install the sensor in a medium which has turbulence specially if bubbles are present?

0 Answers  






What is standard procedure of manual mapping in Radar type level transmitter?

0 Answers  


3element

2 Answers  


I want to know if flowrate increases in 16' pipe line what will happen to upstream pressure and why?

1 Answers  


Are Coils of Electromagnetic flowmeter in direct contact with fluid material

4 Answers   TATA,


What is linearity of RTD over 0 to 200 degC?

1 Answers   Honeywell,


I want to know about DDCMIS in detail ? please explain it. Also give name of reference books in which it is explained in detail in very simple manner.

0 Answers  


What are advantages and disadvantage of the ac supply load cell?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)