For load of 1 nos 3 TR Air Conditioners,6nos of 60 Watt
Tibe Lights, 2 nos 200 W Outdoor Lights,1 no Coffee
maker.All may work at the same timehow do I select DG Set
Rating ,pLease advise the calculations
Answer / vachaspati sharma
your total load is :-
3TR Approx. 3000 watts
60wattx06Nos 360 watts
200Wattx02 Nos 400 watt
Cofee maker Approx 500 watt
total load 4260 watt
say aprrox 5000 watt / 1000watt
5 Kw load
KW= KVA x P.F ( if PF .8)
KVA = KW/.8
5/.8
KVA = 6 ans
| Is This Answer Correct ? | 3 Yes | 1 No |
Why 3 over-current and 1 earth fault relay is used on primary side of transformer? Why 2 over-current and 1 earth fault relay in used on secondary side of transformer?
what are the checks of diesel gensets
what is the function of a commutator in a dc generator?
14 Answers College School Exams Tests, NTPC, TCS,
What is the constructional difference between ceiling fan and table fan
what is the use of earthing?
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
why occ characteristics of generator is also called as magnatization characteristics ?
how do you reduce the skin effect
how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?
why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.....
How we can find the regulation of transformer?
How Many safety of Air circuit breaker
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)