For load of 1 nos 3 TR Air Conditioners,6nos of 60 Watt
Tibe Lights, 2 nos 200 W Outdoor Lights,1 no Coffee
maker.All may work at the same timehow do I select DG Set
Rating ,pLease advise the calculations
Answer / vachaspati sharma
your total load is :-
3TR Approx. 3000 watts
60wattx06Nos 360 watts
200Wattx02 Nos 400 watt
Cofee maker Approx 500 watt
total load 4260 watt
say aprrox 5000 watt / 1000watt
5 Kw load
KW= KVA x P.F ( if PF .8)
KVA = KW/.8
5/.8
KVA = 6 ans
Is This Answer Correct ? | 3 Yes | 1 No |