corona happens more in summer or winter?
Answers were Sorted based on User's Feedback
Answer / kakadiatapan
it will be more there at a time of summer because corona happens due to the breakdown of hot moistured air(less voltage required for breakdown) around the high voltage conductor. in case of summer there will be more temperature with moisture in the atmosphire.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / aashish gambhir
u can see it mathematically...delta which is inversely
proportional to Temp..in summer temp is more...so del is
less....nw crtcl disruptve coltage,Vo is proprtnal to
delta ...so lesser the value of delta lesser the Vo.....and
loss is proportional to (operatng voltage,Vp - Vo)
square..so loss is more
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / murali
most properly corona happens on winter session only
| Is This Answer Correct ? | 11 Yes | 13 No |
what principle the cabel TV channels are transmitted? will you be able to check the power at the connector behind your TV with a tester?If yes what is the supply level?
what is V0/V rating of cable
I am an electrical power engineer and arranged power system for a data center, I installed MCB, ELCB and erthing system TN-C-S. But some times several ELCBs Disconnect circuits at the same time! what may be the reason? (the ELCBs are 25A ,30mA)
What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"
electrical
Three set (each phase contain 2 cable of 400 mmsq CU XLPE AWA) of single core cables are connected to 11 KV motor of 14 MW & the switch gear supplay is taken from 11kv feeder & this supplay taken from 275 KV substation. Problem is one pair cable(L3- 2 cable ) getting very hot & gland melted and damaged in switch gear side. the other two cable haven't any more hot(ambient temp only & L3 haveing 95- 100 Degree C. The same problem happened in 275 KV substation switch gear side also where the supply taken for 11 kv switch gear. But here L2 phese cable had problem. Why it is happening like this?. The cable having temperature different at different location from gland side inthe case of 11KV feeder of 275 kv substation. why ?
Can we get the shock if Power system is unearth means delta type take an rated voltage as 6.6 KV?
Why does amplifier gain reduce?
HOW DOES ONE SELECT A TRANSFORMER PHASOR GROUP IE, WHETHER A STAR-DELTA TR OR A STAR-STAR OR A DELTA-DELTA, ETC. TRANSFORMER IS MORE SUITABLE FOR A PARTICULAR KIND OF LOAD OR WORKING CONDITION???
reason behind why the reverse power relay of incoming machine was not acted even when no load was shifted on incoming machine after synchronising the machines ?
What is relation bet kvar & microfarad
Types of test in Switchgears, MCC, NGR and DB's how it should be procced. Can anyone give me the details here or email me to pasuvaraj.k@gmail.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)