what difference between tapping -15% to +5 % and -5% to
+15% tap. & how can define HV turns on maximun & minimum
tap of power transformer.
Answers were Sorted based on User's Feedback
Answer / dinesh
it is the percentage of voltage variation... suppose u take
-15 to +5 means,
From 100% of the transformer voltage u can increase 5%(105%) or decrease 15% (85%).... + defines increase and - defines decrease...
This is done by varying the number of turns by the OLTC...
and the next question, suppose u have 400 turns at 100% then at +5% it is 420 turns and -15% means 340 turns.....
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / k.prakashchandra
That is correct.As the tapping is done on primary side, with
+5% tap you are decreasing secondary voltage by 5% or you
use that tap when the primary voltage increases by 5% to
maintain the secondary voltage steady.Then N1/N2 = 105/100
Is This Answer Correct ? | 3 Yes | 1 No |
how caculate the pump head to maintain perticuler pressure of water and what would be the motor size in hp for the same?
Can transformer develop three phase power from a single phase source?
What is the Difference Between MCCB & ACB & VCB
Why is the earth socket in an electrical plug outlet made thicker and lenghty?
What is spill current in protection relays?
please explian how may types of maintenance works.
How can we measure and monitor critical performance parameters of Diesel Generator Sets, both electrical and engine ?
I do wonder why current is present in neutral wire?i check single phase lead current feeding air conditioner...on its phase its current was 10A while same was 10A in neutral...as we know in neutral voltage is zero so if voltage is zero then how current appears on amp meter? my second observation is (just imagination)when I touch phase wire it give me shock but when i touch neutral nothing happens although as above its carrying current(amps) third but with same logic...as in simple Alternate current sine curve there is + and there is negative peak.means every time phase changing so how come every time same phase and same neutral stand (pardon for english mistakes)
why wound rotor is star-connected?
Incoming line 11kv And transformer capacity is 2500kva. Consumption load is 1300A. Then fuse capacity is 11kv line.
Why the magneti fields are not passes from southpole to north pole
What is gross error?