Can We Apply DC POWER To Transformer????
And Why????
Answers were Sorted based on User's Feedback
Answer / nithin shaju
Applying DC power to a transformer will not step up/down
the voltage,since the current reaches its peak within
milliseconds and remain constant.Therefore no induction
happens.So secondary voltage is induced only during the
current growing period (millisec).After that as long as
there is no fluctuation, sec voltage will be 0.
There is no
problem in connecting dc power suppply to a
transformer.Only winding resistance is taken into
account.But if the current is too high there is a chance of
burning the insulation.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / uma
When the transformer is used with dc excitation, flux rises to the point where magnetic saturation occurs, causing a large increase in magnetizing current & overheating of the transformer. therefore they operate in ac.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / venkat
we cannot apply DC power to transformer as it is an ac machine and on applying DC power the windings of the transformer gets short circuited due to unidirectional flow of electric charge
| Is This Answer Correct ? | 4 Yes | 5 No |
Answer / ahmed
We can apply dc supply to transformer, but here impedance
is only resistance in casof DC.large amount of current will
flow through the promary windings depending on the
magnitude of primary voltage applied.Secondary will not
induce any voltage.
| Is This Answer Correct ? | 4 Yes | 5 No |
What will happen if the 50HZ Transformer is connected with 60HZ power Supply
How do i calculate sizing of transformer on didstrubution load for high rise building.What should be MVA Rating of MV Panel feding by 122 kv.
whether the generating voltage can be made to be transmitted by means of signals to the recieved end or at the consumers end?
Why we use less dia. fuse and conductors at H.T. side, although we use higher dia. cables on L.t. side?
what is the general Classification of Generators
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
In Power transformer oil temperature or winding temperature will be high
hi frienda We have 250kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
what is x'mer ,isolation x'mer & yltra-isolation x'mer?????
how open delta PT works & what is its construction?
OHMS LAW
What is mean by power factor?
18 Answers Shreem Electric Ltd,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)