there is a line fault some where on the ove head
distribution line. how will i locate the fault for clearing
it? ofcourse i have to megger the line but what information
makes me clear that the fault is in that section of the
line?
Answers were Sorted based on User's Feedback
Answer / abhidewas
its very simple. just go through the section whose relay has tripped the circuit breaker.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / aamod tripathi.
The fault if is in a over head distribution line it is
generally taken care by the protection system (Relays/
CBs)This gives the answer of your question as What
Information makes it clear that the fault is in that section
of line. And as the protection system is quite selective (It
is its important feature while selecting the protection)
Even then if fault occours in Line (Not Cable) The visual
inspection is carried out once the span is known. (Generally
Open Circuit (Breaking of conductor)or short circuit (LG,
LLG,LL fault has occoured due to insulation failure or tree
fallen, or Snake, or Bird)
If it is a cable Megger is the best option to use. The
solution is to join the cable (Not Done Generally) or to
replace it.
For information: THE CABLE IS THUS REQUIRED TO FACE THE
MAXIMUM NUMBER OF TESTS AFTER MANUFACTURING. AS WE DONT
INSTALL ANY BACKUP FOR CABLE.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is the conductor size in 33/11 kv line
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
what is sf6 where it is use & working or function ?
I am using submission of two ct in one and half scheme for 67/67N protection. Both CTs star point is grounded separately near ct box.Will two point ground give wrong tripping to 67/67N during fault or no matter.
how to calculate the current carrying capacity of cable
On a 10 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 65 AH). What Shall be the current rating of DC MCB ?
6 Answers RR, TNEB Tamil Nadu Electricity Board,
Which motor is 3.3 or 11kV more reliable, in terms of efficeancy,maintenance, reliability.
0 Answers Megatron Solutions, TCL,
when we r using 3.5 cable for a bldg. and put laod on each phase using the neutral and neutral is the return paht for the phase so the current of the neutral must be Ir+Ib+iY (return).But the size of the netural is .5 as comper to the phase.
what happen when power factor of 2 parallely operated transformer become equle?
What is the problem of internal failure in ship engine telegraph system norcontrol?
pls,send the previous year written test questions.
why ferranti efect occurs on no load only?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)