Answer / satish tumbare
above answer is not write.Density also affect level
| Is This Answer Correct ? | 17 Yes | 2 No |
well....suppose if you want to measure level of a
tank....connect your PG at the the bottom of the tank.for
eg. if your PG shows 5ksc pressure. then 5ksc is approx.
equal to 50000 mm WC..which is approx. 50 mtr.so level in
the tank would approx. 50 mtr.
| Is This Answer Correct ? | 19 Yes | 7 No |
Height(level)=Pressure / sp.gravity.
So,if u fix the pressure gauge at the bottom tapping of the tank.the pressure reading is divided with the sp.gravity of the liquid in the tank.
you can cross check by measuring the level and multiplying it with sp.gravity
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / anish kumaran.r
Using purge tube method you can measure the level by a PG and a air regulator. But it needs suppy air. Make a 'T' setup and connect gauge at one end ,supply air at one end and another end should be inserted in to the tank where the level to be measured. The gauge shows t level of the tank we shd convert into mmwc.
Regards,
R.Anish kumaran,
C&I Engineer,
Thermax ltd.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / anwar ali
We have to know the tank if it open or closed tank. Then we can use Hydro-static Head Pressure Theory. And of course the type of liquid (density) because the pressure depend upon of the highest and density of the liquid:
P = d x h
It is important if the tank is used as storage or there inside it some physic changing.
Anther important thing to put in our mind if the measuring system used is suppression or elevator range.
That all what we need measure level
| Is This Answer Correct ? | 0 Yes | 0 No |
How to calibrate a orifice differential pressure flow transmitter in process?
In RTU Panel we are having several Analogue & Digital Inputs /Outputs. We are recently facing some problems over Analog inputs , which are not updating properly (But Digital Input are updating normally) Can any one tell me from where the problem is creating , we have checked PLC CPU card, Analog Input card & we reconfigured ,But still the issue is there. Issue : 1. Sometimes Analog values are updating & sometimes not. 2. Analog values are not updating normally , showing some wrong Values 3. Total dead (0 value) Analog values are Level & flow measurement from the field instruments. (But in field the instruments are working normally & Displaying the values normally in local display unit) This problem we are facing in our Water Plant. If any one experienced this same problem or having any ideas related to our issue PLS send your valuable Answers/Replies...
Difine flashing , Cavitaion & Noise? how to minimize these effects
what is radar type level transmitters and its basic principle and how to calibrate it
Explain the difference between plc and cnc?
What is differnece between leveltroll and interface leveltrol?
please any body have most important data for study for saudi aramco test of instrument QC thanks email shahnaveedullah@gmail.com
Yokogawa dcs nodes advantages?
what is dry leg and what is wet leg?
What is DCS and PLC scanning time?
Dead weight tester & comparator for calibration , which is more accurate , what is the application.
1 Answers Bapco Bahrain Petroleum Company,
what should he know if he is an assitent engineer instrumentation in cement industries of experience of 10 - 15 year.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)