If load current is 70amps or 50amps what range of CT to
install for ampere metering
Answers were Sorted based on User's Feedback
Answer / maprayil
Always go for the CT primary suitable for about 40% higher
currents of the load current. So if the load current is
70A, you should opt for a CT primary of 98A, say 100A.
Secondary current rating of the CT will be dependent on the
input requirements of the measuring instrument (meter)/
Controller. Many such meters specially calls for an input
of 5A or 1A. Certain meters have the option to select 5A
or 1A input based on the secondary current of the CT.
| Is This Answer Correct ? | 10 Yes | 1 No |
CT range is 70/5A because it caluculates min to max current
| Is This Answer Correct ? | 1 Yes | 2 No |
State norton’s theorem?
what is DRP panels?
what is differance bw ELCB and MCB. ?
What is error of a measurement?
What is the effect of positive feedback on stability of the system?
how to calculate transformer turn primary & secondary side 11kv to 420v
power transmission pole used one support , that only for support or earthing
what is the difference between star and delta connection?
what is the difference between id fans and fd fans
12 Answers Perkins Thermal Systems,
whate is the meaning of balance/unbalance,in stabilizers type
Is it possible to use AC supply insted of DC supply in trip coil operation? if not, why?
how to select earthing wire? procedures and parameters?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)