why we need of power factor correction? give advantages
Answers were Sorted based on User's Feedback
Answer / nagaraju thangella
The powerfactor plays an important role in AC Since pwr consumed depends on PF
A PF Less than unity results in
Larger kva rating of equipment.
Larger copper losses
Poor voltage regulation
Reduced handling capacity
KW=KVA Cos phi
Hence we correct power factor
Is This Answer Correct ? | 13 Yes | 2 No |
Answer / majid dadjoo
with reactive power corection you can decrease reactive
power on line . it means that by reducing reactive
power ,same active power can transmit by a line with lower
current than previous.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / gms
adding to the above explanation we can say it is required to maintain a flat voltage profile in the line and control the flow of reactive power
Is This Answer Correct ? | 1 Yes | 0 No |
How would you supply power to a village which is very far from a sub-station and has only a 11kV line running near by?
bsec exam syllabus (mis)
why rating of generator is kva but motor is kw ?
if we use a normal natural thundering; than approx how much amount of electricity we generate?
in control panel, how can i measuring the distance between one bus bar to another bus bar. then now only for bus bar. in mpcb and contactor also. that means one mpcb to another mpcb how much distance? how can i calculate that.
In Extended Delta transformer, by which method we can measure the extended angle of transformer?
IN 6.6KV 3 phase switch gear .i will give 6.6kv to R phase only to earth in during H.v testing (through H.v KIT).what happen remaining phases.how much voltage get remaining phases.why? explain.
What is meant by field loss in a DC motor?
Can any body tell gulf interview question for experienced electrical engineer ?
Whether the over frequency protection is turbine or alternator and why?
what is the working principale of air circuit breaker ?
An AC coil to give DC supply whats happen in the coil.what type of problem are create.