why secondary of c.t. will kept open ?
Answers were Sorted based on User's Feedback
Answer / raj
secondary should not be kept open... your question is wrong.
either it should be connected to measuring device or must be
shorted and grounded properly in order to avoid blast.
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / siddu
it will cause dangerously high secondary voltage and wen it s energized it should be loaded.
| Is This Answer Correct ? | 5 Yes | 0 No |
The secondary of ct is never open. It is always in a closed
circuit as connected to another coil that produces magnetic
force to cause deflection (The more current passing thru
the primary is the more magnitude of force to cause
deflection to the needle) to the needle used in reading
amperes such as ammeter thus serving the purpose of ct, to
be able to measure current.
| Is This Answer Correct ? | 11 Yes | 8 No |
Answer / rushi913@gmail.com
resultant voltge will increse and possibility of damaging
the winding will be occure which will be dangerous for man
who are operating this instrument
| Is This Answer Correct ? | 6 Yes | 5 No |
what is the minimum clearance between a 11KV 150KVAR capacitor cell and series reactor.can a series reactor can be mounted in the same structure of the capacitor cells structure
how to get more than 1000 ohms between 2 earth pits ?
Technical requirement of Copper earthing over GI earthing.
Vaccum circuit breaker
how to extend relay operating timing in 24V dc relay card (without using Timer )
why the rating of dc generator is in kw where as rating of alternator is in kva?
How to calculate the cable size (XLPE)for suitable to 120KW load (if Motor or heaters etc)
what is the technical diffrences of mccb and acb
if grounding is notdone at regular intervals for long distance transmission, will the load connected at distribution end receive voltage during negativehalf cycle of the sine wave?
how much the voltage & resistance should be ,between earth & neutral points.?& why?
RATING OF LIGHTENING ARRESTER FOR 11 KV LINE IS 9 KV is ok ,but haw to calculate the KA rating?
how to maintain frenquncy with syncronising sub-station for distribution
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)