hi frienda We have 250kva cater pillet dg set we are fasing
one diffrent proublam in dg we are start dg set after one
mint applying load around 450a load but dg was run 3 Or 4
mints after 3 mints dg was shuding down automatic how to
face this proublam pls tel any budy
Answers were Sorted based on User's Feedback
Answer / abdulgafar
A full load current of 250KVA DG Set is approximatly 350A.
Most of the DG Sets are designed to catter approximatly 10%
over load For a period of one hour hence a 250KVA dg set
can catter 385A For a period of one hour. you have applied
more load then the DG Set can catter/ deliver hence your DG
Set is triping automatically after about 3 min. hope i have
answered your question.
AGM
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / ajay
that is 250kva d.g.it will be give only 250-300amps
load...you will also give to 300a load and then check it
OR
hydrollic magnatising is very low,d.g.will run there
after voltage is not buildup,then d.g.is shuting down...
please do one thing short your battery
terminals and then give to connection it will be started.
| Is This Answer Correct ? | 0 Yes | 0 No |
how to calculate the earth fault current
what is the technical diffrences of mccb and acb
difference between buscoupler & bussection?
how can we change the phase angle b/w two phase?
open circuit test when performed on double the voltage & double the freq, then what will happen with p.f and current magnitude?
how to calculate total load in a villa?
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
How i can calculate current of cable according to ares?
When capacitor bank connect on line. It's draw some current but it's current not increase of main line ammeter. Why?
My ups output shows 230 v between phase and neutral,but show zero between phase and earth.Is the system/installation is correct.If not what will be the possible reasons
how do you test the capacitor bank ?
Is there any local or International standards that prohibit the installation of earthing pit in the planters area where the earthing pit is subject to continues soak in water?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)