While connecting the flood light plug on to the 415 V
distribution panel,there was spark and the cable got burnt.
Three ignitors of the flood light also burnt of. The lamps
are of 400 W (total 6 lamps) connected through 1.5 mm2
cable. The plug was immediately removed from the circuit.
There was a 30 mA RCD connected and a 250 A MCCB; however
both did not trip. What could be the possible reasons for
the circuit devices not to trip?Can someone assist please.
Additional info if needed can be provided.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
It appears that you have connected a phase instead of neutral.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / albaloshi4u
check flood light another distribution box whether your flood light is working properly or faulty and also check your db phase voltage.
Is This Answer Correct ? | 0 Yes | 0 No |
how to use single phase supply for a three phase equipement.
what is meant by neutral Ct of a transformer and how it connected in transformer
how to calculate fuse rating for a motor
How to calculate cable size in HT AND LT
reason behind why the reverse power relay of incoming machine was not acted even when no load was shifted on incoming machine after synchronising the machines ?
defination of loads
why ct's&pt'S out put called as burden,why compelsary short ckt the secondary of ct's while removing the burden?
Whether the over frequency protection is turbine or alternator and why?
what will happen if i connect the buchholz relay in reverse direction.
i have a roll dia aprox.43 inches and gear box ratio is 14.3.so my question is how was decide the kw rating of motor.
why neutral should connect to earth in delta-star type transformer
what solid earthing means?