What will be the size of cable required for 5.5 KW motor (
Full load current 10 Amps approx.), Starting current with
DOL is 120 Amps. Aprrox. Short circuit current with LLLG
fault is 2000 Amps Approx.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
6 sq mm copper cable and 10 sq mm if the usage is
non-stop.cables can withstand heavy currents for short periods.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / birinchi87
4 sq. mm is sufficient. In our plant we are using 2.5 sq. mm for 5.5 KW and 4 sq. mm for 11 KW.
| Is This Answer Correct ? | 18 Yes | 11 No |
Why the core of a underground cable is spiral in shape instead of straight??
400Kv,can it be generated?why?
which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?
CAN ANYBODY EXPLAIN WHAT ACTUALLY MEAN BY THE PHASE DEFFRENCE? R,L,C CIRCUITS?
Why don't we use ground free electricity to avoid electric shock.As birds are do not get shock.
what is the difference between MCCB and SFU in terms of their application?
2 Answers Secure Meters, Tata Teleservices,
why we connect dg neutral with ground?
Differnce between earthing and nuetral
In how we connect watt meter for open & short circuit test of a single phase transformer.
WHY WE USE CABLE JUNCTION AFTER BETWEEN TANSMISSION LINE AND TRANSFORMER
domine+aptitude test means?
How core saturation effects the secondary voltage (whats the theory) of a current transformer in service?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)